H3C S6116 Ultra-Low Latency Switch Series Configuration Guide-Release 671x-6W100
HomeSupportSwitchesS6116 SeriesConfigure & DeployConfiguration GuidesH3C S6116 Ultra-Low Latency Switch Series Configuration Guide-Release 671x-6W100
25-PTP configuration
25-PTP configuration 363.74 KB
Configuring PTP·· 1
About PTP· 1
Basic concepts· 1
Grandmaster clock selection and master-member/subordinate relationship establishment 3
Synchronization mechanism·· 3
Protocols and standards· 5
Restrictions and guidelines: PTP configuration· 5
PTP tasks at a glance· 6
Configuring PTP (IEEE 1588 version 2) 6
Specifying PTP for obtaining the time· 6
Specifying a PTP profile· 7
Configuring clock nodes· 7
Specifying a clock node type· 7
Configuring an OC to operate only as a member clock· 7
Specifying a PTP domain· 8
Enabling PTP globally· 8
Enabling PTP on a port 8
Configuring PTP ports· 9
Configuring the role of a PTP port 9
Configuring the mode for carrying timestamps· 9
Specifying a delay measurement mechanism for a BC or an OC· 10
Configuring one of the ports on a TC+OC clock as an OC-type port 10
Configuring PTP message transmission and receipt 11
Setting the interval for sending announce messages and the timeout multiplier for receiving announce messages  11
Setting the interval for sending Pdelay_Req messages· 11
Setting the interval for sending Sync messages· 12
Setting the minimum interval for sending Delay_Req messages· 12
Configuring parameters for PTP messages· 13
Specifying the IPv4 UDP transport protocol for PTP messages· 13
Configuring a source IP address for multicast PTP messages transmitted over UDP· 13
Configuring a destination IP address for unicast PTP messages transmitted over UDP· 14
Configuring the MAC address for non-Pdelay messages· 14
Disabling PTP path tracing· 15
Adjusting and correcting clock synchronization· 15
Setting the delay correction value· 15
Calculating the TAI based on the UTC time· 15
Configuring a priority for a clock· 16
Display and maintenance commands for PTP· 16
PTP configuration examples· 17
Example: Configuring PTP (IEEE 1588 version 2, IEEE 802.3/Ethernet transport, multicast transmission) 17
Example: Configuring PTP (IEEE 1588 version 2, IPv4 UDP transport, multicast transmission) 20
Configuring PTP
About PTP
Precision Time Protocol (PTP) provides time synchronization among devices with submicrosecond accuracy. It provides also precise frequency synchronization.
Basic concepts
PTP profile
PTP profiles (PTP standards) include:
·     IEEE 1588 version 2—1588v2 defines high-accuracy clock synchronization mechanisms. It can be customized, enhanced, or tailored as needed. 1588v2 is the latest version.
·     IEEE 802.1AS—802.1AS is introduced based on IEEE 1588. It specifies a profile for use of IEEE 1588-2008 for time synchronization over a virtual bridged local area network (as defined by IEEE 802.1Q). 802.1AS supports only point-to-point full-duplex Ethernet, IEEE 802.11, and IEEE 802.3 EPON links.
·     SMPTE ST 2059-2—ST2059-2 is introduced based on IEEE 1588. It specifies a profile specifically for time synchronization of audio or video equipment in a professional broadcast environment. It includes a self-contained description of parameters, their default values, and permitted ranges.
The switch does not support the IEEE 802.1AS or SMPTE ST 2059-2 PTP profile.
PTP domain
A PTP domain refers to a network or part of a network that is enabled with PTP. A PTP domain has only one reference clock called "grandmaster clock (GM)." All devices in the domain synchronize to the clock.
Clock node and PTP port
A node in a PTP domain is a clock node. A port enabled with PTP is a PTP port. PTP defines the following types of basic clock nodes:
·     Ordinary Clock (OC)—A PTP clock with a single PTP port in a PTP domain for time synchronization. It synchronizes time from its upstream clock node through the port. If an OC operates as the clock source, it sends synchronization time through a single PTP port to its downstream clock nodes.
·     Boundary Clock (BC)—A clock with more than one PTP port in a PTP domain for time synchronization. A BC uses one of the ports to synchronize time from its upstream clock node. It uses the other ports to synchronize time to the relevant upstream clock nodes. If a BC operates as the clock source, such as BC 1 in Figure 1, it synchronizes time through multiple PTP ports to its downstream clock nodes.
·     Transparent Clock (TC)—A TC does not keep time consistency with other clock nodes. A TC has multiple PTP ports. It forwards PTP messages among these ports and performs delay corrections for the messages, instead of performing time synchronization. TCs include the following types:
¡     End-to-End Transparent Clock (E2ETC)—Forwards all PTP packets in the network and supports calculation of the delay on the entire link.
¡     Peer-to-Peer Transparent Clock (P2PTC)—Forwards only Sync, Follow_Up, and Announce messages, terminates other PTP messages, and supports calculation of the delay on the entire link.
Figure 1 shows the positions of these types of clock nodes in a PTP domain.
Figure 1 Clock nodes in a PTP domain
In addition to these basic types of clock nodes, PTP introduces hybrid clock nodes. For example, a TC+OC has multiple PTP ports in a PTP domain. One port is the OC type, and the others are the TC type.
A TC+OC forwards PTP messages through TC-type ports and performs delay corrections. In addition, it synchronizes time through its OC-type port. TC+OCs include these types: E2ETC+OC and P2PTC+OC.
Master-member/subordinate relationship
The master-member/subordinate relationship is automatically determined based on the Best Master Clock (BMC) algorithm. You can also manually specify a role for the clock nodes.
The master-member/subordinate relationship is defined as follows:
·     Master/Member node—A master node sends a synchronization message, and a member node receives the synchronization message.
·     Master/Member clock—The clock on a master node is a master clock (parent clock) The clock on a member node is a member clock.
·     Master/Subordinate port—A master port sends a synchronization message, and a subordinate port receives the synchronization message. The master and subordinate ports can be on a BC or an OC.
·     Grant-port/request-port—The IEEE 1588 version 2 PTP profile supports unicast negotiation. To configure unicast negotiation, you can specify PTP ports as request-ports or grant-ports. A grant-port grants and provides PTP service. A request-port requests and receives PTP service. Typically, a grant-port is in master state. A request-port is in slave state when selected as the port for time synchronization and in listening state when not selected
A port that neither receives nor sends synchronization messages is a passive port.
Clock source type
A clock node uses the local clock source, which is 38.88 MHz clock signals generated by a crystal oscillator inside the clock monitoring module.
Grandmaster clock
As shown in Figure 1, the grandmaster clock (GM) is the ultimate source of time for clock synchronization in a PTP domain. It is elected automatically by the clock nodes in the PTP domain. The clock nodes exchange PTP messages and elect the GM by comparing the clock priority, time class, and time accuracy carried in the PTP messages.
You can also specify a GM manually.
A GM can be manually specified. It can also be elected through the BMC algorithm as follows:
1.     The clock nodes in a PTP domain exchange announce messages and elect a GM by using the following rules in descending order:
a.     Clock node with higher priority 1.
b.     Clock node with higher time class.
c.     Clock node with higher time accuracy.
d.     Clock node with higher priority 2.
e.     Clock node with a smaller port ID (containing clock number and port number).
The master nodes, member nodes, master ports, and subordinate ports are determined during the process. Then a spanning tree with the GM as the root is generated for the PTP domain.
2.     The master node periodically sends announce messages to the member nodes. If the member nodes do not receive announce messages from the master node, they determine that the master node is invalid, and they start to elect another GM.
After master-member relationships are established between the clock nodes, the master and member clock nodes exchange PTP messages and record the message transmit and receive time. Based on the timestamps, each member clock calculates the path delay and time offset between them and the master clock and adjusts their time accordingly for time synchronization with the master clock.
PTP defines two path delay measurement mechanisms: Request_Response_ and Peer Delay, both of which are based on network symmetry.
Request_Response
The Request_Response mechanism measures the average path delay between the master and member clock nodes by using the PTP messages as shown in Figure 2. A TC between master and member clock nodes does not calculate the path delay. It forwards PTP messages and carries the Sync message residence time on it to the downstream clock node.
This mechanism can be implemented in one of the following two modes:
·     Two-step mode—t1 is carried in the Follow_Up message as shown in Figure 2.
·     Single-step mode—t1 is carried in the Sync message, and no Follow_Up message is sent.
Figure 2 shows the Request_Response mechanism in two-step mode.
1.     The master clock sends a Sync message to the member clock, and records the sending time t1. Upon receiving the message, the member clock records the receiving time t2.
2.     After sending the Sync message, the master clock immediately sends a Follow_Up message that carries time t1.
3.     The member clock sends a Delay_Req message to the master clock, and records the sending time t3. Upon receiving the message, the master clock records the receiving time t4.
4.     The master clock returns a Delay_Resp message that carries time t4.
After this procedure, the member clock obtains all the four timestamps and can make the following calculations:
·     Round-trip delay between the master and member clocks: (t2 – t1) + (t4 – t3)
·     One-way delay between the master and member clocks: [(t2 – t1) + (t4 – t3)] / 2
·     Offset between the member and master clocks: (t2 – t1) – [(t2 – t1) + (t4 – t3)] / 2 or [(t2 – t1) – (t4 – t3)] / 2
Figure 2 Request_Response mechanism (two-step node)
Peer Delay
The Peer Delay mechanism measures the average path delay between two clock nodes. The two clock nodes (BC, TC, or OC) implementing this mechanism send Pdelay messages to each other, and calculate the one-way link delay between them independently. The message interaction process and delay calculation method are identical on the two nodes. TCs that exist between master and member clock nodes divide the synchronization path into multiple links and participate in delay calculation. The link delays and Sync message residence time on the TCs are carried to downstream nodes.
·     Two-step mode
As shown in Figure 3, Pdelay messages include Pdelay_Req, Pdelay_Resp, and Pdelay_Resp_Follow_Up messages. t2 is carried in the Pdelay_Resp message, and t3 is carried in the Pdelay_Resp_Follow_Up message.
·     Single-step mode:
Pdelay messages include Pdelay_Req and Pdelay_Resp messages. t3 – t2 is carried in the Pdelay_Resp, and no Pdelay_Resp_Follow_Up message is sent.
Figure 3 uses Clock node B as an example to describe the Peer Delay mechanism.
1.     Clock node B sends a Pdelay_Req message to Clock node A, and records the sending time t1. Upon receiving the message, Clock node A records the receiving time t2.
2.     Clock node A sends a Pdelay_Req message that carries t2 to Clock node B, and records the sending time t3. Upon receiving the message, Clock node B records the receiving time t4.
3.     Clock node A immediately sends a Pdelay_Resp_Follow_Up message carrying t3 to Clock node B after sending the Pdelay_Req message.
After this procedure, Clock node B obtains all the four timestamps and can make the following calculations:
·     Round-trip delay between Clock node A and Clock node B: (t2 – t1) + (t4 – t3)
·     One-way delay between Clock node A and Clock node B: [(t2 – t1) + (t4 – t3)] / 2 = [(t4 – t1) – (t3 – t2)] / 2
·     Time offset between the member clock and the master clock: Sync message receiving time on the member clock – Sync message sending time on the master clock – Total one-way delays on all links – Total Sync message residence time on all TCs.
Figure 3 Peer Delay mechanism (two-step mode)
·     IEEE Std 1588-2008, IEEE Standard for a Precision Clock Synchronization Protocol for Networked Measurement and Control Systems, 2008
·     IEEE 802.1AS, Timing and Synchronization for Time-Sensitive Applications in Bridged Local Area Networks
·     SMPTE ST 2059-2, SMPTE Profile for Use of IEEE-1588 Precision Time Protocol in Professional Broadcast Applications
Only the management Ethernet interface supports PTP.
Before configuring PTP, determine the PTP profile and define the scope of the PTP domain and the role of every clock node.
As a best practice, specify the BC or OC clock node type for the devices as a best practice. A TC clock node is mainly used for forwarding PTP messages. When receiving a PTP message, a TC multicasts the message from all its PTP interfaces except the inbound interface of the PTP message. To deploy a TC, plan the TC location and number and location of PTP interfaces on the TC manually to prevent PTP forwarding loops.
The PTP time might jump and get unlocked if it is synchronized with the NTP time or system time, both of which have a lower precision. As a best practice, use PTP for time synchronization when PTP is enabled on the device.
1.     Specifying PTP for obtaining the time
2.     Specifying a PTP profile
Specify the IEEE 1588 version 2 PTP profile.
3.     Configuring clock nodes
¡     Specifying a clock node type
¡     (Optional.) Configuring an OC to operate only as a member clock
4.     Specifying a PTP domain
5.     Enabling PTP.
For PTP to run on an interface, enable PTP globally and on the interface.
¡     Enabling PTP globally
¡     Enabling PTP on a port
6.     Configuring PTP ports
¡     (Optional.) Configuring the role of a PTP port
¡     Configuring the mode for carrying timestamps
¡     Specifying a delay measurement mechanism for a BC or an OC
¡     Configuring one of the ports on a TC+OC clock as an OC-type port
7.     (Optional.) Configuring PTP message transmission and receipt
¡     Setting the interval for sending announce messages and the timeout multiplier for receiving announce messages
¡     Setting the interval for sending Pdelay_Req messages
¡     Setting the interval for sending Sync messages
¡     Setting the minimum interval for sending Delay_Req messages
8.     (Optional.) Configuring parameters for PTP messages
¡     Specifying the IPv4 UDP transport protocol for PTP messages
¡     Configuring a source IP address for multicast PTP messages transmitted over UDP
¡     Configuring a destination IP address for unicast PTP messages transmitted over UDP
¡     Configuring the MAC address for non-Pdelay messages
¡     Disabling PTP path tracing
9.     (Optional.) Adjusting and correcting clock synchronization
¡     Setting the delay correction value
¡     Calculating the TAI based on the UTC time
10.     (Optional.) Configuring a priority for a clock
2.     Specify PTP for obtaining the time.
clock protocol ptp
By default, the device uses NTP to obtain the system time.
For more information about the clock protocol command, see device management commands in the command reference for the device.
You must specify a PTP profile before configuring PTP settings. Changing the PTP profile clears all settings under the profile.
2.     Specify a PTP profile.
ptp profile 1588v2
By default, no PTP profile is configured, and PTP is not running on the device.
Before you specify a clock node type, specify a PTP profile.
If the ptp unicast-forward enable command has been configured, you can specify only the E2ETC clock node type for the device.
Changing or removing the clock node type restores the default settings of the PTP profile.
2.     Specify a clock node type for the device.
ptp mode { bc | e2etc | e2etc-oc | oc | p2ptc | p2ptc-oc }
By default, no clock node type is specified.
An OC can operate either as a master clock to send synchronization messages or as a member clock to receive synchronization messages. This task allows you to configure an OC to operate only as a member clock.
If an OC is operating only as a member clock, you can use the ptp force-state command to configure its PTP port as a master port or passive port.
This task is applicable only to OCs.
2.     Configure the OC to operate only as a member clock.
ptp slave-only
By default, an OC operates as a master or member clock.
Within a PTP domain, all devices follow the same rules to communicate with each other. Devices in different PTP domains cannot exchange PTP messages.
2.     Specify a PTP domain for the device.
ptp domain value
By default, no PTP domain exists.
For PTP to run on an interface, you must enable PTP globally and on the interface.
2.     Enable PTP globally.
ptp global enable
By default, PTP is enabled globally.
A port enabled with PTP becomes a PTP port.
You can enable PTP on only one port on an OC.
2.     Enter management Ethernet interface view.
3.     Enable PTP on the port.
ptp enable
By default, PTP is disabled on a port.
You can configure the master, passive, or slave role for a PTP port.
For an OC that operates in slave-only mode, you can perform this task to change its PTP port role to master or slave.
You can configure one subordinate port on the device.
3.     Configure the role of the PTP port.
ptp force-state { master | passive | slave }
By default, the PTP port role is automatically calculated through BMC.
4.     Return to system view.
5.     Activate the port role configuration.
ptp active force-state
By default, the port role configuration is not activated.
Timestamps can be carried in either of the following modes:
·     Single-step mode—The Sync message (in the Request_Response or Peer Delay mechanism) and Pdelay_Resp message (in the Peer Delay mechanism) carry their sending timestamps by themselves.
·     Two-step mode—The Sync message (in the Request_Response or Peer Delay mechanism) and Pdelay_Resp message (in the Peer Delay mechanism) do not carry their sending timestamps by themselves. The subsequent messages carry their sending timestamps.
The device does not support the single-step timestamp-carrying mode in the current software version.
3.     Configure the mode for carrying timestamps.
ptp clock-step { one-step | two-step }
By default, the two-step mode is used for carrying  timestamps.
PTP defines two transmission delay measurement mechanisms: Request_Response and Peer Delay. For correct communication, ports on the same link must share the same delay measurement mechanism.
Follow these restrictions and guidelines when you configure this task:
·     You can configure this task only when the PTP clock node type is BC or OC.
·     You cannot configure this task when the PTP clock node type is E2ETC, E2ETC+OC, P2PTC, or P2PTC+OC. The E2ETC and E2ETC+OC clock nodes support both the request-response and peer delay measurement mechanisms. The P2PTC clock node supports only the peer delay measurement mechanism.
3.     Specify a delay measurement mechanism for a BC or an OC.
ptp delay-mechanism { e2e | p2p }
By default, the request-response delay measurement mechanism applies.
All ports on a TC+OC (E2ETC+OC or P2PTC+OC) are TC-type ports by default. This feature allows you to configure one of the ports on a TC+OC clock as an OC-type port.
This task is applicable only to E2ETC+OCs and P2PTC+OCs.
For time synchronization accuracy, the OC-type port on an E2ETC+OC or P2PTC+OC must be specified as the master port.
3.     Configure the port type as OC.
ptp port-mode oc
By default, the port type for all ports on a TC+OC is TC.
A master node periodically sends announce messages at the specified interval. If a member node does not receive any announce message from the master node after the timeout expires, it determines that the master node is invalid. The timeout = timeout multiplier × interval at which the master node sends announce messages.
The interval at which the master node sends announce messages depends on whether unicast negotiation is enabled.
·     If unicast negotiation is not enabled, the master node uses the value configured by using the ptp announce-interval command on its interface as the interval.
·     If unicast negotiation is enabled, you must configure the interval on the request-port of the client. The request-port uses the configured interval to negotiate with the grant-port on the server for the interval at which the grant-port sends announce messages to the client. If the negotiation succeeds, the grant-port sends announce messages at the configured interval to the client. If the negotiation fails, the grant-port does not send announce messages to the client.
3.     Set the interval for sending announce messages.
ptp announce-interval interval
By default, the interval argument value is 1 and the interval for sending announce messages is 2 (21) seconds.
4.     Set the number of intervals before a timeout occurs.
ptp announce-timeout multiple-value
By default, a timeout occurs when three intervals are reached.
3.     Set the interval for sending Pdelay_Req messages.
ptp pdelay-req-interval interval
By default, the interval argument value is 0 and the interval for sending peer delay request messages is 1 (20) second.
The master node sends Sync messages to the member nodes periodically. The interval at which the master node sends Sync messages to member nodes depends on whether unicast negotiation is enabled.
·     If unicast negotiation is not enabled, use  this task to configure the interval on the master node.
·     If unicast negotiation is enabled, you must configure the interval on the request-port of the client. The request-port uses the configured interval to negotiate with the grant-port on the server for the interval at which the grant-port sends Sync messages to the client. If the negotiation succeeds, the grant-port sends Sync messages at the configured interval to the client. If the negotiation fails, the grant-port does not send Sync messages to the client.
3.     Set the interval for sending Sync messages.
ptp syn-interval interval
By default, the interval argument value is 0 and the interval for sending Sync messages is 1 (20) second.
When receiving a Sync or Follow_Up message, an interface can send Delay_Req messages only when the minimum interval is reached. This task allows you to set the minimum interval for sending Delay_Req messages.
In PTP multicast transport mode, this setting takes effect only when configured on the master clock. The master clock sends the value to a member clock through PTP messages to control the interval for the member clock to send Delay_Req messages. To view the interval, execute the display ptp interface command on the member clock.
In PTP unicast transport mode, this setting takes effect when configured on member clocks. It does not take effect when configured on the master clock.
3.     Set the minimum interval for sending Delay_Req messages.
ptp min-delayreq-interval interval
The interval argument value is 0 and the minimum interval for sending delay request messages is 1 (20) second.
PTP messages can be transported over IEEE 802.3/Ethernet or IPv4 UDP.
Software and feature compatibility
This feature is supported only in E6709 and later.
3.     Specify the IPv4 UDP transport protocol for PTP messages.
ptp transport-protocol udp
By default, PTP messages are transported over IEEE 802.3/Ethernet.
To transport multicast PTP messages over UDP, you must configure a source IP address for the messages.
If both a source IP address for multicast PTP messages transmitted over UDP and a destination address for unicast PTP messages transmitted over UDP are configured, the system unicasts the messages.
2.     Configure a source IP address for multicast PTP messages transmitted over UDP.
ptp source ip-address
By default, no source IP address is configured for multicast PTP messages transmitted over UDP.
To transport unicast PTP messages over UDP, you must configure a destination IP address for the messages.
Configure an IP address for the current interface, and make sure the interface and the peer PTP interface can reach each other.
3.     Configure a destination IP address for unicast PTP messages transmitted over UDP.
ptp unicast-destination ip-address
By default, no destination IP address is configured for unicast PTP messages transmitted over UDP.
Pdelay messages include Pdelay_Req, Pdelay_Resp, and Pdelay_Resp_Follow_Up messages. The destination MAC address of Pdelay messages is 0180-C200-000E by default, which cannot be modified. The destination MAC address of non-Pdelay messages is either 0180-C200-000E or 011B-1900-0000.
This feature takes effect only when PTP messages are encapsulated in IEEE 802.3/Ethernet packets.
3.     Configure the destination MAC address for non-Pdelay messages.
ptp destination-mac mac-address
The default destination MAC address is 011B-1900-0000.
PTP path tracing traces the clock nodes that the clock signals traverse from the GM to the device. The system can obtain complete path tracing information only when all clock nodes on the path are enabled with PTP path tracing. If a device on the path does not support PTP path tracing, disable this feature to prevent PTP intercommunication issues.
2.     Disable PTP path tracing.
ptp path-trace disable
By default, PTP path tracing is enabled.
PTP performs time synchronization based on the assumption that the delays in sending and receiving messages are the same. However, this is not practical. If you know the offset between the delays in sending and receiving messages, you can set the delay correction value for more accurate time synchronization.
3.     Set a delay correction value.
ptp asymmetry-correction { minus | plus } value
The default is 0 nanoseconds. Delay correction is not performed.
International Atomic Time (TAI) is a high-precision atomic coordinate time scale. Coordinated Universal Time (UTC) is based on TAI and adjusted by leap seconds for synchronization with astronomical time.
UTC is constantly compared with UT1 (astronomical time, reflecting the earth's rotation). The International Bureau of Weights and Measures (BIPM) will notify to add or subtract one second from the UTC time scale at the last minute on a specific date (typically June 30 or December 31) to ensure that the difference between UTC and UT1 is within one second.
The BIPM publishes the difference between UTC and TAI periodically. Till now, UTC is 37 seconds behind TAI.
Internet devices typically use the UTC time. To provide more accurate time, PTP also uses TAI. If the device acts as a subordinate clock node, it uses the UTC time and TAI time of the clock reference. If the device acts as the clock reference, it will calculate the TAI time based on the UTC time, and synchronize the UTC and TAI time to the subordinate clocks. This task is used to calculate the TAI time based on the UTC time.
TAI = Current UTC + cumulative offset + leap second that might occur in the future. To get the correct TAI time from the UTC time,
·     Set the accurate UTC time on the device.
·     Use the ptp utc offset command to set the cumulative offset of UTC relative to TAI as published by BIPM. This command takes effect immediately.
·     If the BIPM notifies to add or subtract one second from the UTC time scale on a specific data after you use the ptp utc offset command to configure the cumulative offset of TAI relative to UTC, use the ptp utc { leap59-date | leap61-date } date command to change the UTC time. The TAI time will be changed accordingly.
This setting takes effect only when it is configured on the master clock node and the local clock of the master clock node is the GM.
Configure this feature on both the master and member nodes for the new master clock to provide accurate TAI time after a master/member node switchover.
2.     Set the cumulative offset of UTC relative to TAI.
ptp utc offset utc-offset
The default is 0 seconds.
3.     Add or subtract one second from the UTC time scale at the last minute on the specified date.
By default, no second is added or subtracted from the UTC time.
Priorities for clocks are used to elect the GM. The smaller the priority value, the higher the priority.
2.     Configure the priority for the specified clock for GM election through BMC.
ptp priority clock-source local { priority1 priority1 | priority2 priority2 }
By default, the priority 1 and priority 2 values are both 128.
Display PTP clock information.
display ptp clock
Display the delay correction history.
display ptp corrections
Display information about foreign master nodes.
display ptp foreign-masters-record [ interface interface-type interface-number ]
Display PTP information on an interface.
display ptp interface [ interface-type interface-number ]
Display brief PTP information on all interfaces.
display ptp interface brief
Display brief information about the PTP synchronization path from the GM to the device.
display ptp path-trace
Display parent node information for the PTP device.
display ptp parent
Display historical role change information for PTP ports.
display ptp port-history [ interface interface-type interface-number ]
Display PTP statistics.
display ptp statistics [ interface interface-type interface-number ]
Display PTP clock time properties.
display ptp time-property
Clear PTP statistics.
reset ptp statistics [ interface interface-type interface-number ]
As shown in Figure 4, configure PTP (IEEE 1588 version 2, IEEE 802.3/Ethernet transport, multicast transmission) to enable time synchronization between the devices.
·     Specify the IEEE 1588 version 2 PTP profile and the IEEE 802.3/Ethernet transport protocol for PTP messages on Device A, Device B, and Device C.
·     Assign Device A, Device B, and Device C to the same PTP domain. Specify the OC clock node type for Device A and Device C, and E2ETC clock node type for Device B. All clock nodes elect a GM through BMC in the PTP domain.
·     Use the default Request_Response delay measurement mechanism on Device A and Device C.
You can use the device as Device A or Device C, and cannot use it as Device B.
Figure 4 Network diagram
1.     Configure Device A:
# Specify the IEEE 1588 version 2 PTP profile.
[DeviceA] ptp profile 1588v2
# Specify the OC clock node type.
[DeviceA] ptp mode oc
# Create a PTP domain.
[DeviceA] ptp domain 0
# Enable PTP globally.
[DeviceA] ptp global enable
# Specify PTP for obtaining the time.
[DeviceA] clock protocol ptp
# Configure the priority of the timing signal acquired via PTP as 1.
[DeviceA] network-clock source ptp priority 1
# Enable PTP on M-GigabitEthernet 0/0/0.
[DeviceA] interface m-gigabitethernet 0/0/0
[DeviceA-M-GigabitEthernet0/0/0] ptp enable
[DeviceA-M-GigabitEthernet0/0/0] quit
2.     Configure Device B:
[DeviceB] ptp profile 1588v2
# Specify the E2ETC clock node type.
[DeviceB] ptp mode e2etc
[DeviceB] ptp domain 0
[DeviceB] ptp global enable
[DeviceB] clock protocol ptp
# Enable PTP on Ten-GigabitEthernet 1/0/1.
[DeviceB-Ten-GigabitEthernet1/0/1] ptp enable
# Enable PTP on Ten-GigabitEthernet 1/0/2.
[DeviceB] interface ten-gigabitethernet 1/0/2
[DeviceB-Ten-GigabitEthernet1/0/2] ptp enable
[DeviceB-Ten-GigabitEthernet1/0/2] quit
3.     Configure Device C:
<DeviceC> system-view
[DeviceC] ptp profile 1588v2
[DeviceC] ptp mode oc
[DeviceC] ptp domain 0
[DeviceC] ptp global enable
[DeviceC] clock protocol ptp
[DeviceC] network-clock source ptp priority 1
[DeviceC] interface m-gigabitethernet 0/0/0
[DeviceC-M-GigabitEthernet0/0/0] ptp enable
[DeviceC-M-GigabitEthernet0/0/0] quit
When the network is stable, perform the following tasks:
·     Use the display ptp clock command to display PTP clock information.
·     Use the display ptp interface brief command to display brief PTP running information for all PTP interfaces.
# Display PTP clock information on Device A.
[DeviceA] display ptp clock
PTP global state    : Enabled
PTP profile         : IEEE 1588 Version 2
PTP mode            : OC
Slave only          : No
Lock status         : Locked
Clock ID            : 000FE2-FFFE-FF0000
Clock type          : Local
Clock domain        : 0
Number of PTP ports : 1
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
 Offset (log variance) : 65535
Offset from master : 0 (ns)
Mean path delay    : 0 (ns)
Steps removed      : 0
Local clock time   : Sun Jan 15 20:57:29 2019
# Display brief PTP running information for all PTP interfaces on Device A.
[DeviceA] display ptp interface brief
Name           State         Delay mechanism  Clock step  Asymmetry correction
MGE0/0/0       Master        E2E              Two         0
# Display PTP clock information on Device B.
[DeviceB] display ptp clock
PTP mode            : E2ETC
Slave only          : No
Clock ID            : 000FE2-FFFE-FF0001
Clock type          : Local
Clock domain        : 0
Number of PTP ports : 2
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Offset from master  : N/A
Mean path delay     : N/A
Steps removed       : N/A
# Display brief PTP running information for all PTP interfaces on Device B.
[DeviceB] display ptp interface brief
Name       InstID    State         Delay mechanism  Clock step  Asymmetry correction
XGE1/0/1   0         N/A           E2E              Two         0
XGE1/0/2   0         N/A           E2E              Two         0
The command outputs show that Device A is elected as the GM and M-GigabitEthernet 0/0/0 on Device A is the master port.
As shown in Figure 5, configure PTP (IEEE 1588 version 2, IPv4 UDP transport, multicast transmission) to enable time synchronization between the devices.
·     Specify the IEEE 1588 version 2 PTP profile for Device A, Device B, and Device C.
·     Specify multicast IPv4 UDP transport for PTP messages.
·     Assign Device A, Device B, and Device C to the same PTP domain. Specify the OC clock node type for Device A and Device C, and P2PTC clock node type for Device B. All clock nodes elect a GM through BMC in the PTP domain.
·     Specify the peer delay measurement mechanism (p2p) for Device A and Device C.
Figure 5 Network diagram
# Configure the source IP address for multicast PTP messages transmitted over IPv4 UDP.
[DeviceA] ptp source 10.10.1.1
# On M-GigabitEthernet 0/0/0, specify the IPv4 UDP transport protocol for PTP messages, specify the delay measurement mechanism as p2p, and enable PTP.
[DeviceA-M-GigabitEthernet0/0/0] ptp transport-protocol udp [DeviceA-M-GigabitEthernet0/0/0] ptp delay-mechanism p2p
# Specify the P2PTC clock node type.
[DeviceB] ptp mode p2ptc
# Configure the source IP address for multicast PTP messages transmitted over UDP.
[DeviceB] ptp source 10.10.2.1
# On Ten-GigabitEthernet 1/0/1, specify the IPv4 UDP transport protocol for PTP messages and enable PTP.
DeviceB-Ten-GigabitEthernet1/0/1] ptp transport-protocol udp
# On Ten-GigabitEthernet 1/0/2, specify the IPv4 UDP transport protocol for PTP messages and enable PTP.
[DeviceB-Ten-GigabitEthernet1/0/2] ptp transport-protocol udp
[DeviceC] ptp source 10.10.3.1
[DeviceC-M-GigabitEthernet0/0/0] ptp transport-protocol udp [DeviceC-M-GigabitEthernet0/0/0] ptp delay-mechanism p2p
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : 0
MGE0/0/0        Master        P2P              Two         0
PTP mode            : P2PTC
Slave only          : No
Lock status         : Unlocked
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed       : N/A
XGE1/0/1   0          N/A           P2P              Two         0
XGE1/0/2   0          N/A           P2P              Two         0
