Configuring Modbus

About Modbus

Modbus is an open, standardized, easy-to-use, and reliable communication protocol in the industrial field. It enables client/server communication between devices connected to different types of buses or networks, suitable for automation control scenarios. Currently, the Modbus protocol is widely used for communication among various control devices in automation control systems, instruments, robot control, and mobile device control. Modbus holds a significant position especially in smart manufacturing and industrial internet fields.

Benefits

Modbus provides the following benefits:

·     The Modbus protocol standards are openly available, allowing for data exchange between devices from different manufacturers.

·     Modbus, an application layer protocol, defines message structures that can be understood and used by industrial controllers and does not define the physical layer, enabling data transmission within various network architectures. Modbus not only supports multiple electrical interfaces such as RS485 and TCP/IP, but also transmits data through various media including twisted pair cables and optical fibers.

·     The Modbus protocol has a simple and easy-to-understand message format, which facilitates user understanding and usage, as well as development and integration by manufacturers in industrial control networks.

Modbus network model

Modbus communication layer

Modbus supports deployment on a serial link or an Ethernet TCP/IP network. It utilizes network layers for communication in different networks as shown in Figure 1.

Figure 1 Modbus communication layer

Modbus communication mechanism

As shown in Figure 2, Modbus uses a client/server structure. In Modbus communication, only the client sends requests, and the server responds to the requests. Data is transmitted between the client and server over Modbus. On an industrial control network, PLC devices typically act as clients, and peripheral I/O sensors, valves, network drives, or other measuring devices act as servers.

Figure 2 Modbus network model

Modbus data model

With the Modbus protocol, a Modbus client can perform read/write operations on the data stored in a Modbus server to perform data analysis and state control over the industrial network.

As shown in Figure 3, Modbus assigns logical address ranges for various device applications, with each application having a unique range. When the Modbus client requests data, it only needs to provide the Modbus server with the start address and the length of the desired data, and the server can then accurately send the requested data back to the client.

Figure 3 Communication mechanism

For information about Modbus-TCP address mappings for H3C devices, see "Appendix Modbus-TCP address mappings."

Modbus transmission messages

Modbus has two types of transmission messages, Modbus-RTU messages and Modbus-TCP messages.

Modbus-RTU messages

In Modbus-RTU transmission mode, the format of the Application Data Unit (ADU) uses the structure, as shown in Figure 4.

Figure 4 Modbus-RTU ADU

The fields in the Modbus-RTU ADU structure are as follows:

·     Server address—Address of the server, which is the target of the Modbus request sent by the client. The address length is one byte.

·     Function code—Instruction sent by the client to the server, such as reading/writing data from the server. The instruction length is one byte.

·     Function-specific data—Describes the content of a specific request or response instruction based on different function codes. The data length varies.

·     Error checking—Checks the correctness of the received data to avoid errors during message transmission. The filed length is two bytes.

Modbus-TCP messages

In Modbus-TCP transmission mode, the format of the Application Data Unit (ADU) uses the structure, as shown in Figure 5.

Figure 5 Modbus-TCP ADU

Different from Modbus messages transmitted over a serial link, the Modbus-TCP ADU does not require an error checking field, as the TCP/UDP protocols inherently provide error checking capabilities. In addition, the Modbus-TCP ADU no longer needs an address field; and addressing is achieved via encapsulation through the network and data link layers on the Ethernet network. To distinguish Modbus messages on the Ethernet network, a Modbus Application Header (MBAP) is encapsulated onto the PDU of the Modbus-TCP ADU. The fields in the Modbus-TCP ADU are as follows:

·     Transaction identifier—Identifies the transaction of the Modbus request or response. The field length is two bytes.

·     Protocol identifier—Value 0 identifies the Modbus protocol. The field length one byte.

·     Length identifier—Identifies the subsequent field length. The field length is two bytes.

·     Unit identifier—Used for system internal routing, identifying the remote servers connected via serial links or other buses, The field length is one byte.

·     Function code—Instruction sent by the client to the server, such as reading/writing data from the server. The instruction length is one byte.

·     Function-specific data—Describes the content of a specific request or response instruction based on different function codes. The data length varies.

Restrictions and guidelines: Modbus configuration

H3C industrial switches can act only as Modbus servers in a Modbus network.

This feature is not supported in an IRF fabric.

Enabling Modbus-TCP for the device

About this task

With this feature enabled, an H3C device can establish a TCP connection with a Modbus client and communicates with that client through Modbus-TPC. H3C devices uses port 502 to establish TCP connections with Modbus clients. H3C industrial switches can enable or disable a port and obtain port, ring network, and alarm information through Modbus-TCP.

By default, a Modbus client can read and write information from the device through Modbus TCP. Changing the device status without permission can pose a severe security risk. To address this issue, you can execute this command to set the operating mode of Modbus TCP on the device to read only, allowing Modbus clients to only read information from the device through Modbus TCP.

To obtain Modbus data addresses mapped to ports on devices, execute the display modbus-tcp information interface command.

Restrictions and guidelines

A Modbus client can read and edit the status of a maximum of 128 ports on an H3C device.

Procedure

1.     Enter system view.

system-view

2.     Enable Modbus-TCP for the device.

modbus-tcp enable

By default, Modbus-TCP is disabled for the device.

3.     (Optional.) Set the operating mode of Modbus-TCP to read only.

modbus-tcp working-mode read-only

By default, Modbus-TCP operates in read write mode. The device can read its information and edit its status through Modbus-TCP.

Display and maintenance commands for Modbus

Execute display commands in any view.

 

Task

Command

Display information required for the device to read local port information using the Modbus-TCP protocol.

display modbus-tcp information interface { interface-type interface-number | interface-name }

Appendix Modbus-TCP address mappings

Device information (0X0000-0X0FFF)

Node name

Start address (hex)

Data length

(Unit: words)

Data type

Description

Example

Company Name

0x0000

255

ASCII

Company name

Company Name = “H3C”

Word 0 Hi byte = ‘H’

Word 0 Lo byte = ‘3’

Word 1 Hi byte = ‘C’

Word 1 Lo byte = ‘\0’

Word 2 Hi byte = ‘\0’

Word 2 Lo byte = ‘\0’

Dev Type

0x0100

255

ASCII

Product name

Device Type = “SWITCH”

Word 0 Hi byte = ‘S’

Word 0 Lo byte = ‘W’

Word 1 Hi byte = ‘I’

Word 1 Lo byte = ‘T’

Word 2 Hi byte = ‘C’

Word 2 Lo byte = ‘H’

Word 3 Hi byte = ‘\0’

Word 3 Lo byte = ‘\0’

Company location

0x0200

257

ASCII

Company location

Location = “Hangzhou, China”

Word 0 Hi byte = ‘H’

Word 0 Lo byte = ‘a’

Word 1 Hi byte = ‘n’

Word 1 Lo byte = ‘g’

Word 2 Hi byte = ‘z’

Word 2 Lo byte = ‘h’

Word 3 Hi byte = ‘o’

Word 3 Lo byte = ‘u’

Word 4 Hi byte = ‘,’

Word 4 Lo byte = ‘ ’ (space)

Word 5 Hi byte = ‘C’

Word 5 Lo byte = ‘h’

Word 6 Hi byte = ‘i’

Word 6 Lo byte = ‘n

Word 7 Hi byte = ‘a’

Word 7 Lo byte = ‘\0’

Word 8 Hi byte = ‘\0’

Word 8 Lo byte = ‘\0’

Contact

0x0400

257

ASCII

Contact

 Contact

 = “New H3C Technologies Co., Ltd”

Word 0 Hi byte = ‘N’

Word 0 Lo byte = ‘e’

Word 1 Hi byte = ‘w’

Word 1 Lo byte = ‘ ’ (space)

Word 2 Hi byte = ‘H’

Word 2 Lo byte = ‘3’

Word 3 Hi byte = ‘C’

Word 3 Lo byte = ‘ ’ (space)

Word 4 Hi byte = ‘T’

Word 4 Lo byte = ‘e’

Word 5 Hi byte = ‘c’

Word 5 Lo byte = ‘h’

Word 6 Hi byte = ‘n’

Word 6 Lo byte = ‘o’

Word 7 Hi byte = ‘l’

Word 7 Lo byte = ‘o’

Word 8 Hi byte = ‘g’

Word 8 Lo byte = ‘i

Word 9 Hi byte = ‘e’

Word 9 Lo byte = ‘s’

Word 10 Hi byte = ‘ ’ (space)

Word 10 Lo byte = ‘C’

Word 11 Hi byte = ‘o’

Word 11 Lo byte = ‘.’

Word 12 Hi byte = ‘,’

Word 12 Lo byte = ' '(space)

Word 13 Hi byte = ‘L’

Word 13 Lo byte = ‘t’

Word 14 Hi byte = ‘d’

Word 14 Lo byte = ‘.’

Word 15 Hi byte = ‘\0’

Word 15 Lo byte = ‘\0’

Product Type

0x0600

129

ASCII

Product category

Product Type

 = “H3C IE4320-52S”

Word 0 Hi byte = ‘H’

Word 0 Lo byte = ‘3’

Word 1 Hi byte = ‘C’

Word 1 Lo byte = ‘ ’ (space)

Word 2 Hi byte = ‘I’

Word 2 Lo byte = ‘E’

Word 3 Hi byte = ‘4’

Word 3 Lo byte = ‘3’

Word 4 Hi byte = ‘2’

Word 4 Lo byte = ‘0’

Word 5 Hi byte = ‘-’

Word 5 Lo byte = ‘5’

Word 6 Hi byte = ‘2’

Word 6 Lo byte = ‘S

Word 7 Hi byte = ‘\0’

Word 7 Lo byte = ‘\0’

Serial Num

0x0690

17

ASCII

Serial number

Serical Num =  “219801A2DD9209Q00009”

Word 0 Hi byte = ‘2’

Word 0 Lo byte = ‘1’

Word 1 Hi byte = ‘9’

Word 1 Lo byte = ‘8’

Word 2 Hi byte = ‘0’

Word 2 Lo byte = ‘1’

Word 3 Hi byte = ‘A’

Word 3 Lo byte = ‘2’

Word 4 Hi byte = ‘D’

Word 4 Lo byte = ‘D’

Word 5 Hi byte = ‘9’

Word 5 Lo byte = ‘2’

Word 6 Hi byte = ‘0’

Word 6 Lo byte = ‘9’

Word 7 Hi byte = ‘Q’

Word 7 Lo byte = ‘0’

Word 8 Hi byte = ‘0’

Word 8 Lo byte = ‘0’

Word 9 Hi byte = ‘0’

Word 9 Lo byte = ‘9’

Word 10 Hi byte = ‘\0’

Word 10 Lo byte = ‘\0’

Bootware Version

0x06B0

32

ASCII

BootWare version

Bootware Version = “150”

Word 0 Hi byte = ‘1’

Word 0 Lo byte = ‘5’

Word 1 Hi byte = ‘0’

Word 1 Lo byte = ‘\0’

Word 2 Hi byte = ‘\0’

Word 2 Lo byte = ‘\0’

Software Version

0x06D0

32

ASCII

Software version

Bootware Version = “7.1.070 Release 6350”

Word 0 Hi byte = ‘7’

Word 0 Lo byte = ‘.’

Word 1 Hi byte = ‘1’

Word 1 Lo byte = ‘.’

Word 2 Hi byte = ‘0’

Word 2 Lo byte = ‘7’

Word 3 Hi byte = ‘0’

Word 3 Lo byte = ‘ ’

Word 4 Hi byte = ‘R’

Word 4 Lo byte = ‘e’

Word 5 Hi byte = ‘l’

Word 5 Lo byte = ‘e’

Word 6 Hi byte = ‘a’

Word 6 Lo byte = ‘s’

Word 7 Hi byte = ‘e’

Word 7 Lo byte = ‘ ’

Word 8 Hi byte = ‘6’

Word 8 Lo byte = ‘3’

Word 9 Hi byte = ‘5’

Word 9 Lo byte = ‘0’

Word 10 Hi byte = ‘\0’

Word 10 Lo byte = ‘\0’

Hardware Version

0x06F0

128

ASCII

Hardware version

Hardware Version = “Ver.A”

Word 0 Hi byte = ‘V’

Word 0 Lo byte = ‘e’

Word 1 Hi byte = ‘r’

Word 1 Lo byte = ‘.’

Word 2 Hi byte = ‘A’

Word 2 Lo byte = ‘\0’

Word 3 Hi byte = ‘\0’

Word 3 Lo byte = ‘\0’

Logical Version

0x0770

20

ASCII

Logical version

N/A

IP Addr

0x0800

2

HEX

IP address

IP address=1.2.3.4

Word 0 Hi byte = 0x01

Word 0 Lo byte = 0x02

Word 1 Hi byte = 0x03

Word 1 Lo byte = 0x04

Start Mac

0x0802

3

HEX

MAC address of the device

MAC address=98F1-81CD-434A

Word 0 Hi byte = 0x98

Word 0 Lo byte = 0xf1

Word 1 Hi byte = 0x81

Word 1 Lo byte = 0xcd

Word 0 Hi byte = 0x43

Word 0 Lo byte = 0x4a

MAC Number

0x0805

2

HEX

Number of MAC addresses of the MPU

MAC quantity=56

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x00

Word 1 Lo byte = 0x38

Power1 State

0x0807

1

HEX

·     1—up

·     0—down

Power supply 1 status is up=1

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Power2 State

0x0808

1

HEX

·     1—up

·     0—down

Power supply 1 status is down=0

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

Cpu Long Usage

0x0809

2

HEX

Average CPU usage (%) of the device in 5 minutes

CPU usage=6%

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x00

Word 1 Lo byte = 0x06

Cpu Short Usage

0x080B

2

HEX

Average CPU usage (%) of the device in 1 minute

CPU usage=4%

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x00

Word 1 Lo byte = 0x04

Mem Size Total

0x080D

2

HEX

Total memory size of the device (KB)

Total memory size of the device=506408

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x07

Word 1 Hi byte = 0xba

Word 1 Lo byte = 0x28

Mem Free

0x080F

2

HEX

Free memory of the device (KB)

Total memory size of the device=176376

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x02

Word 1 Hi byte = 0xb0

Word 1 Lo byte = 0xf8

Run Time

0x0811

4

HEX

Current time (UTC)

Uptime=1357233936

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x00

Word 1 Lo byte = 0x00

Word 2 Hi byte = 0x50

Word 2 Lo byte = 0xe5

Word 3 Hi byte = 0xbf

Word 3 Lo byte = 0x10

Run Time Total

0x0815

4

HEX

Total uptime of the device (min)

Total uptime=982

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x00

Word 1 Lo byte = 0x00

Word 2 Hi byte = 0x00

Word 2 Lo byte = 0x00

Word 3 Hi byte = 0x03

Word 3 Lo byte = 0xd6

Temperature

0x0819

2

HEX

Device temperature (°C)

N/A

Port information (1-32) (0X1000-0X1FFF)

Node name

Start address (hex)

Data length

(Unit: words)

Data type

Description

Example

IfName

0x1000

32

ASCII

Name of the port (length: 2-47)

IfDescr =

“GigabitEthernet2/0/2”

Word 0 Hi byte = ‘G’

Word 0 Lo byte = ‘i’

Word 1 Hi byte = ‘g’

Word 1 Lo byte = ‘a’

Word 2 Hi byte = ‘b’

Word 2 Lo byte = ‘i’

Word 3 Hi byte = ‘t’

Word 3 Lo byte = ‘E’

Word 4 Hi byte = ‘t’

Word 4 Lo byte = ‘h’

Word 5 Hi byte = ‘e’

Word 5 Lo byte = ‘r’

Word 6 Hi byte = ‘n’

Word 6 Lo byte = ‘e’

Word 7 Hi byte = ‘t’

Word 7 Lo byte = ‘2’

Word 8 Hi byte = ‘/’

Word 8 Lo byte = ‘0’

Word 9 Hi byte = ‘/’

Word 9 Lo byte = ‘2’

Word 10 Hi byte = ‘\0’

Word 10 Lo byte = ‘\0’

IfStatus

0x1040

1

HEX

read:

·     0—disable

·     1—up

·     2—down

A port is enabled if it is in up or down state

write:

·     1—enable

·     2—disable

Port state down:

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

IfSpeed

0x1041

1

HEX

·     0—Auto

·     1—2Mbps

·     2—10Mbps

·     3—100Mbps

·     4—155Mbps

·     5—622bps

·     6—1Gbps

·     7—2Gbps

·     8—2.5Gbps

·     9—4Gbps

·     10—5Gbps

·     11—8Gbps

·     12—10Gbps

·     13—16Gbps

·     14—20Gbps

·     15—25Gbps

·     16—32Gbps

·     17—40Gbps

·     18—100Gbps

1G port speed:

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x06

Duplex

0x1042

1

HEX

·     1—Full

·     2—Half

·     3—Auto

Full duplex mode:

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

FlowControl

0x1043

1

HEX

·     1—Enable

·     2—Disable

Flow control enabled:

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

InPkts

0x1044

4

HEX

Number of received packets

Total number of received packets on the port: 10359115

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x9e

Word 0 Hi byte = 0x11

Word 0 Lo byte = 0x4b

InOctets

0x1048

4

HEX

Number of received bytes (byte)

Total number of received bytes: 1325966720

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x4F

Word 0 Lo byte = 0x08

Word 0 Hi byte = 0xA5

Word 0 Lo byte = 0x80

OutPkts

0x104C

4

HEX

Number of sent packets

Number of sent packets: 21919

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x55

Word 0 Lo byte = 0x9F

OutOctets

0x1050

4

HEX

Number of sent bytes (byte)

Total number of sent bytes: 1470550

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x16

Word 0 Hi byte = 0x70

Word 0 Lo byte = 0x56

InUcastPkts

0x1054

4

HEX

Number of received unicast packets

Number of received unicast packets: 5641988

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x56

Word 0 Hi byte = 0x17

Word 0 Lo byte = 0x04

InMulticastPkts

0x1058

4

HEX

Number of received multicast packets

Number of received multicast packets: 2605221

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x27

Word 0 Hi byte = 0xC0

Word 0 Lo byte = 0xA5

InBrdcastPkts

0x105C

4

HEX

Number of received broadcast packets

Number of received broadcast packets: 2111906

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x20

Word 0 Hi byte = 0x39

Word 0 Lo byte = 0xA2

OutUcastPkts

0x1060

4

HEX

Number of sent unicast packets

Number of sent unicast packets: 21234

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x52

Word 0 Lo byte = 0xF2

OutMulticastPkts

0x1064

4

HEX

Number of sent multicast packets

Number of sent multicast packets: 4998

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x13

Word 0 Lo byte = 0x86

OutBrdcastPkts

0x1068

4

HEX

Number of sent broadcast packets

Number sent broadcast packets: 3329

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x0D

Word 0 Lo byte = 0x01

InPauses

0x106C

4

HEX

Number of received pause frames

Number of received pause frames: 680

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x02

Word 0 Lo byte = 0xA8

OutPauses

0x1070

4

HEX

Number of sent pause frames

Number of sent pause frames: 680

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x02

Word 0 Lo byte = 0xA8

InErrCRCFrames

0x1074

4

HEX

Number of received CRC error packets

Number of received CRC error packets: 2872808

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x2B

Word 0 Hi byte = 0xD5

Word 0 Lo byte = 0xE8

 

 

NOTE:

·     The start port ID is 1.

·     The node data address for each port (1-32) = node start address + 0x80 * (port ID - start port ID).

 

Port information (33-64) (0X2000-0X2FFF)

Node name

Start address (hex)

Data length

(Unit: words)

Data type

Description

Example

IfDescr

0x2000

32

ASCII

Name of the port (length: 2 to 47)

IfDescr =

“GigabitEthernet2/0/2”

Word 0 Hi byte = ‘G’

Word 0 Lo byte = ‘i’

Word 1 Hi byte = ‘g’

Word 1 Lo byte = ‘a’

Word 2 Hi byte = ‘b’

Word 2 Lo byte = ‘i’

Word 3 Hi byte = ‘t’

Word 3 Lo byte = ‘E’

Word 4 Hi byte = ‘t’

Word 4 Lo byte = ‘h’

Word 5 Hi byte = ‘e’

Word 5 Lo byte = ‘r’

Word 6 Hi byte = ‘n’

Word 6 Lo byte = ‘e’

Word 7 Hi byte = ‘t’

Word 7 Lo byte = ‘2’

Word 8 Hi byte = ‘/’

Word 8 Lo byte = ‘0’

Word 9 Hi byte = ‘/’

Word 9 Lo byte = ‘2’

Word 10 Hi byte = ‘\0’

Word 10 Lo byte = ‘\0’

IfStatus

0x2040

1

HEX

read:

·     0—disable

·     1—up

·     2—down

A port is enabled if it is in up or down state

write:

·     1—enable

·     2—disable

N/A

IfSpeed

0x2041

1

HEX

·     0—Auto

·     1—2Mbps

·     2—10Mbps

·     3—100Mbps

·     4—155Mbps

·     5—622bps

·     6—1Gbps

·     7—2Gbps

·     8—2.5Gbps

·     9—4Gbps

·     10—5Gbps

·     11—8Gbps

·     12—10Gbps

·     13—16Gbps

·     14—20Gbps

·     15—25Gbps

·     16—32Gbps

·     17—40Gbps

·     18—100Gbps

N/A

Duplex

0x2042

1

HEX

·     1—Full

·     2—Half

·     3—Auto

N/A

FlowControl

0x2043

1

HEX

Enable flow

control

·     2—Disable

·     3—Only enable

flow control

packet receiving

N/A

InPkts

0x2044

4

HEX

Number of received packets

N/A

Number of received bytes

InOctets

0x2048

4

HEX

Number of received bytes

N/A

OutPkts

0x204C

4

HEX

Number of sent packets

N/A

OutOctets

0x2050

4

HEX

Number of sent bytes

N/A

InUcastPkts

0x2054

4

HEX

Number of received unicast packets

N/A

InMulticastPkts

0x2058

4

HEX

Number of received multicast packets

N/A

InBrdcastPkts

0x205C

4

HEX

Number of received broadcast packets

N/A

OutUcastPkts

0x2060

4

HEX

Number of sent unicast packets

N/A

OutMulticastPkts

0x2064

4

HEX

Number of sent multicast packets

N/A

OutBrdcastPkts

0x2068

4

HEX

Number of sent broadcast packets

N/A

InPauses

0x206C

4

HEX

Number of received pause frames

N/A

OutPauses

0x2070

4

HEX

Number of sent pause frames

N/A

InErrCRCFrames

0x2074

4

HEX

Number of received CRC error packets

N/A

 

NOTE:

·     The start port ID is 33.

·     The node data address for each port (33-64) = node start address + 0x80 * (port ID - start port ID).

 

Port information (65-96) (0X3000-0X3FFF)

Node name

Start address (hex)

Data length

(Unit: words)

Data type

Description

Example

IfName

0x3000

32

ASCII

Name of the port (length: 2 to 47)

IfDescr =

“GigabitEthernet2/0/2”

Word 0 Hi byte = ‘G’

Word 0 Lo byte = ‘i’

Word 1 Hi byte = ‘g’

Word 1 Lo byte = ‘a’

Word 2 Hi byte = ‘b’

Word 2 Lo byte = ‘i’

Word 3 Hi byte = ‘t’

Word 3 Lo byte = ‘E’

Word 4 Hi byte = ‘t’

Word 4 Lo byte = ‘h’

Word 5 Hi byte = ‘e’

Word 5 Lo byte = ‘r’

Word 6 Hi byte = ‘n’

Word 6 Lo byte = ‘e’

Word 7 Hi byte = ‘t’

Word 7 Lo byte = ‘2’

Word 8 Hi byte = ‘/’

Word 8 Lo byte = ‘0’

Word 9 Hi byte = ‘/’

Word 9 Lo byte = ‘2’

Word 10 Hi byte = ‘\0’

Word 10 Lo byte = ‘\0’

IfStatus

0x3040

1

HEX

read:

·     0—disable

·     1—up

·     2—down

A port is enabled is in up or down state.

write:

·     1—enable

·     2—disable.

Port state down:

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

IfSpeed

0x3041

1

HEX

·     0—Auto

·     1—2Mbps

·     2—10Mbps

·     3—100Mbps

·     4—155Mbps

·     5—622bps

·     6—1Gbps

·     7—2Gbps

·     8—2.5Gbps

·     9—4Gbps

·     10—5Gbps

·     11—8Gbps

·     12—10Gbps

·     13—16Gbps

·     14—20Gbps

·     15—25Gbps

·     16—32Gbps

·     17—40Gbps

·     18—100Gbps

1G port speed:

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x06

Duplex

0x3042

1

HEX

·     1—Full

·     2—Half

·     3—Auto

Full duplex mode:

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

FlowControl

0x3043

1

HEX

·     1—Enable

·     2—Disable

Flow control enabled:

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

InPkts

0x3044

4

HEX

Number of received packets

Total number of received packets: 10359115

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x9e

Word 0 Hi byte = 0x11

Word 0 Lo byte = 0x4b

InOctets

0x3048

4

HEX

Number of received bytes (byte)

Total number of received bytes: 1325966720

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x4F

Word 0 Lo byte = 0x08

Word 0 Hi byte = 0xA5

Word 0 Lo byte = 0x80

OutPkts

0x304C

4

HEX

Number of sent packets

Number of sent packets: 21919

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x55

Word 0 Lo byte = 0x9F

OutOctets

0x3050

4

HEX

Number of sent bytes (byte)

Total number of sent bytes: 1470550

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x16

Word 0 Hi byte = 0x70

Word 0 Lo byte = 0x56

InUcastPkts

0x3054

4

HEX

Number of received unicast packets

Number of received unicast packets: 5641988

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x56

Word 0 Hi byte = 0x17

Word 0 Lo byte = 0x04

InMulticastPkts

0x3058

4

HEX

Number of received multicast packets

Number of received multicast packets: 2605221

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x27

Word 0 Hi byte = 0xC0

Word 0 Lo byte = 0xA5

InBrdcastPkts

0x305C

4

HEX

Number of received broadcast packets

Number of received broadcast packets: 2111906

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x20

Word 0 Hi byte = 0x39

Word 0 Lo byte = 0xA2

OutUcastPkts

0x3060

4

HEX

Number of sent unicast packets

Number of sent unicast packets: 21234

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x52

Word 0 Lo byte = 0xF2

OutMulticastPkts

0x3064

4

HEX

Number of sent multicast packets

Number of sent multicast packets: 4998

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x13

Word 0 Lo byte = 0x86

OutBrdcastPkts

0x3068

4

HEX

Number of sent broadcast packets

Number sent broadcast packets: 3329

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x0D

Word 0 Lo byte = 0x01

InPauses

0x306C

4

HEX

Number of received pause frames

Number of received pause frames: 680

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x02

Word 0 Lo byte = 0xA8

OutPauses

0x3070

4

HEX

Number of sent pause frames

Number of sent pause frames: 680

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x02

Word 0 Lo byte = 0xA8

InErrCRCFrames

0x3074

4

HEX

Number of received CRC error packets

Number of received CRC error packets: 2872808

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x2B

Word 0 Hi byte = 0xD5

Word 0 Lo byte = 0xE8

 

NOTE:

·     The start port ID is 65.

·     The node data address for each port (65-96) = node start address + 0x80 * (port ID - start port ID).

 

Port information (97-128) (0X4000-0X4FFF)

Node name

Start address (hex)

Data length

(Unit: words)

Data type

Description

Example

IfDescr

0x4000

32

ASCII

Name of the port (length: 2 to 47)

IfDescr =

“GigabitEthernet2/0/2”

Word 0 Hi byte = ‘G’

Word 0 Lo byte = ‘i’

Word 1 Hi byte = ‘g’

Word 1 Lo byte = ‘a’

Word 2 Hi byte = ‘b’

Word 2 Lo byte = ‘i’

Word 3 Hi byte = ‘t’

Word 3 Lo byte = ‘E’

Word 4 Hi byte = ‘t’

Word 4 Lo byte = ‘h’

Word 5 Hi byte = ‘e’

Word 5 Lo byte = ‘r’

Word 6 Hi byte = ‘n’

Word 6 Lo byte = ‘e’

Word 7 Hi byte = ‘t’

Word 7 Lo byte = ‘2’

Word 8 Hi byte = ‘/’

Word 8 Lo byte = ‘0’

Word 9 Hi byte = ‘/’

Word 9 Lo byte = ‘2’

Word 10 Hi byte = ‘\0’

Word 10 Lo byte = ‘\0’

IfStatus

0x4040

1

HEX

read:

·     0—disable

·     1—up

·     2—down

A port is enabled is in up or down state.

write:

·     1—enable

·     2—disable.

N/A

IfSpeed

0x4041

1

HEX

·     0—Auto

·     1—2Mbps

·     2—10Mbps

·     3—100Mbps

·     4—155Mbps

·     5—622bps

·     6—1Gbps

·     7—2Gbps

·     8—2.5Gbps

·     9—4Gbps

·     10—5Gbps

·     11—8Gbps

·     12—10Gbps

·     13—16Gbps

·     14—20Gbps

·     15—25Gbps

·     16—32Gbps

·     17—40Gbps

·     18—100Gbps

N/A

Duplex

0x4042

1

HEX

·     1—Full

·     2—Half

·     3—Auto

N/A

FlowControl

0x4043

1

HEX

Enable flow

control

·     2—Disable

·     3—Only enable

flow control

packet receiving

N/A

InPkts

0x4044

4

HEX

Number of received packets

N/A

InOctets

0x4048

4

HEX

Number of received bytes

N/A

OutPkts

0x404C

4

HEX

Number of sent packets

N/A

OutOctets

0x4050

4

HEX

Number of sent bytes

N/A

InUcastPkts

0x4054

4

HEX

Number of received unicast packets

N/A

InMulticastPkts

0x4058

4

HEX

Number of received multicast packets

N/A

InBrdcastPkts

0x405C

4

HEX

Number of received broadcast packets

N/A

OutUcastPkts

0x4060

4

HEX

Number of sent unicast packets

N/A

OutMulticastPkts

0x4064

4

HEX

Number of sent multicast packets

N/A

OutBrdcastPkts

0x4068

4

HEX

Number of sent broadcast packets

N/A

InPauses

0x406C

4

HEX

Number of received pause frames

N/A

OutPauses

0x4070

4

HEX

Number of sent pause frames

N/A

InErrCRCFrames

0x4074

4

HEX

Number of received CRC error packets

N/A

 

NOTE:

·     The start port ID is 97.

·     The node data address for each port (97-128) = node start address + 0x80 * (port ID - start port ID).

 

Alarm information (0X5000-0X5FFF)

Node name

Start address (hex)

Data length

Unit: words

Data type

Description

Example

Remarks

Port Status Alarm

0x5000

1

HEX

·     0—disable

·     1—normal

·     2—alarm

Normal state

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

The alarm data length for each port is 0x10.

The start port ID is 1.

The alarm node data address for each port (1-128) = node start address + 0x10 * (port ID - start port ID).

Port Input Alarm

0x5001

1

HEX

·     1—normal.

·     2—alarm

Normal state

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

Port Output Alarm

0x5002

1

HEX

·     1—normal.

·     2—alarm

Normal state

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

Port Crc Alarm

0x5003

1

HEX

·     1—normal.

·     2—alarm

Normal state

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

Temperature Alarm

0x5800

1

HEX

·     1—normal.

·     2—alarm

Normal state

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

N/A

Cpu Usage Alarm

0x5801

1

HEX

·     1—normal.

·     2—alarm

Normal state

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

N/A

Mem Usage Alarm

0x5802

1

HEX

·     1—normal.

·     2—alarm

Normal state

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

N/A

Power Status Alarm

0x5803

1

HEX

·     0—disable

·     1—normal.

·     2—Alarm for power supply 1

·     3—Alarm for power supply 2

Normal state

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

N/A

 

NOTE:

·     The start port ID is 1.

·     The alarm node data address for each port (1-128) = alarm node start address + 0x10 * (port ID - start port ID).

 

RSTP information (0X6000-0X6FFF)

Node name

Start address (hex)

Data length

Unit: words

Data type

Description

Example

Remarks

RSTP_PROTOCOL_STATUS

0x6000

1

HEX

·     0—disable

·     1—enable

Normal state

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

N/A

RSTP_ROOTBRIAGE_ID

0x6001

4

HEX

Root bridge ID

8 bytes

RootId=0x80004CB302A30100

Word 0 Hi byte = 0x80

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x4c

Word 1 Lo byte = 0xb3

Word 2 Hi byte = 0x02

Word 2 Lo byte = 0xa3

Word 3 Hi byte = 0x01

Word 3 Lo byte = 0x00

N/A

RSTP_BRIAGE_ID

0x6005

4

HEX

Network bridge ID

8 bytes

BridgeId=0x80004CB302A30100

Word 0 Hi byte = 0x80

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x4c

Word 1 Lo byte = 0xb3

Word 2 Hi byte = 0x02

Word 2 Lo byte = 0xa3

Word 3 Hi byte = 0x01

Word 3 Lo byte = 0x00

N/A

RSTP_PRIORITY

0x6009

2

HEX

Priority, in the range of o to 61440

Priority=32768

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x80

Word 1 Lo byte = 0x00

N/A

RSTP_HELLO_TIME

0x600B

2

HEX

Interval for the root device to send BPDUs, in the range of 1 to 10

HelloTime=2

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x00

Word 1 Lo byte = 0x02

N/A

RSTP_MAX_AGE_TIME

0x600D

2

HEX

Max age timer for BPDUs, in the range of 6 to 40

MaxAge = 20

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x00

Word 1 Lo byte = 0x14

N/A

RSTP_FORWARD_DELAY_TIME

0x600F

2

HEX

Forward delay timer, in the range of 4 to 30

ForwardDelay = 15

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 1 Hi byte = 0x00

Word 1 Lo byte = 0x0f

N/A

RSTP_PORT_PROTOCOL_STATUS

0x6020

1

HEX

·     0—disable

·     1—enable

Enabling state

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x01

The data length for each port is 0x10.

The start port ID is 1.

The node data address for each port (1-128) = node start address + 0x10 * (port ID - start port ID).

RSTP_PORT_PRIORITY

0x6021

2

HEX

Port priority, in the range of o to 240

Priority = 128

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x80

RSTP_PATH_COST

0x6023

2

HEX

Path cost, in the range of 0 to 200000000

PathCost = 0

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

RSTP_PORT_ROLE

0x6025

2

HEX

·     0—Disabled port

·     1—Alternate port

·     2—Backup port

·     3—Root port

·     4—Designated port

·     5—Master port

Role = 4

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x04

RSTP_PORT_STATUS

0x6027

2

HEX

·     1—Discarding

·     2—Learning

·     3—Forwarding

State = 3

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x00

Word 0 Hi byte = 0x00

Word 0 Lo byte = 0x03

 

NOTE:

·     The start port ID is 1.

·     The STP data address for each port (1-128) = node start address + 0x10 * (port ID - start port ID).

 

ERPS information (1-7) (0X7000-0x7FFF)

Node name

Start address (hex)

Data length

Unit: words

Data type

Description

Remarks

MODBUS_REG_ADDR_ERPS_PROTOCOL_STATUS

0x7000

1

HEX

·     0—disable

·     1—enable

N/A

ERPS ring ID

MODBUS_REG_ADDR_ERPS_RING_ID

0x7001

1

HEX

The ID is in the range of 1 to 8.

The data length for each ERPS ring is 0x243.

The start ring ID is 1.

The node data address for each ERPS ring = node start address + 0x243 * (ring ID - start ring ID).

MODBUS_REG_ADDR_ERPS_PORT0

0x7002

1

HEX

N/A

N/A

ERPS ring member port

MODBUS_REG_ADDR_ERPS_PORT1

0x7003

1

HEX

N/A

N/A

MODBUS_REG_ADDR_ERPS_INSTANCE_ID

0x7004

1

HEX

Value range: 1 to 64

The data length for each ERPS instance is 0x9.

The start ring ID is 1.

The start instance ID is 1.

The node data address for each ERPS instance = node start address + 0x243 * (ring ID - start ring ID) + 0x9 * (instance ID - start instance ID).

MODBUS_REG_ADDR_ERPS_CONTROL_VLAN

0x7005

1

HEX

Value range: 2 to 4094.

N/A

MODBUS_REG_ADDR_ERPS_NODE_ROLE

0x7006

1

HEX

·     0—owner

·     1—neighbor

·     2—normal

·     3—interconnection

N/A

MODBUS_REG_ADDR_ERPS_NODE_STATE

0x7007

1

HEX

·     0—Undefined

·     1—init

·     2—idle

·     3—protection

·     4—MS

·     5—FS

·     6—Pending

N/A

MODBUS_REG_ADDR_ERPS_INSTANCE_ENABLE_STATUS

0x7008

1

HEX

·     0—false

·     1—true

N/A

MODBUS_REG_ADDR_ERPS_PORT0_PORT_ROLE

0x7009

1

HEX

·     0—RPL

·     1—Non-RPL

·     2—Undefined

N/A

MODBUS_REG_ADDR_ERPS_PORT0_PORT_STATUS

0x700A

1

HEX

·     0—Block

·     1—Up

·     2—Down

·     3—Undefined

N/A

MODBUS_REG_ADDR_ERPS_PORT1

0x700B

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_ERPS_PORT1_PORT_STATUS

0x700C

1

HEX

·     0—Block

·     1—Up

·     2—Down

·     3—Undefined

N/A

 

NOTE:

·     The start ring ID and instance ID are both 1.

·     The node data address for each ring = node start address + 0x243 * (ring ID - start ring ID).

·     The node address for an instance = node start address + (0x243 * (ring ID - start ring ID)) + (0x9 * (instance ID - start instanceID)).

 

ERPS ring information (8) (0X7000-0x8FFF)

Node name

Start address (hex)

Data length

Unit: words

Data type

Description

Remarks

MODBUS_REG_ADDR_ERPS_RING_ID

0x8001

1

HEX

The ID is in the range of 1 to 8.

The data length for each ERPS ring is 0x243.

The start ring ID is 8.

The node data address for each ERPS ring = node start address + 0x243 * (ring ID - start ring ID).

MODBUS_REG_ADDR_ERPS_PORT0

0x8002

1

HEX

N/A

N/A

MODBUS_REG_ADDR_ERPS_PORT1

0x8003

1

HEX

N/A

N/A

MODBUS_REG_ADDR_ERPS_INSTANCE_ID

0x8004

1

HEX

Value range: 1 to 64

The data length for each ERPS instance is 0x9.

The start ring ID is 8.

The start instance ID is 1.

The node data address for each ERPS instance = node start address + 0x243 * (ring ID - start ring ID) + 0x9 * (instance ID - start instance ID).

MODBUS_REG_ADDR_ERPS_CONTROL_VLAN

0x8005

1

HEX

Value range: 2 to 4094

N/A

MODBUS_REG_ADDR_ERPS_NODE_ROLE

0x8006

1

HEX

·     0—owner

·     1—neighbor

·     2—normal

·     3—interconnection

N/A

MODBUS_REG_ADDR_ERPS_NODE_STATE

0x8007

1

HEX

·     0—Undefined

·     1—init

·     2—idle

·     3—protection

·     4—MS

·     5—FS

·     6—Pending

N/A

MODBUS_REG_ADDR_ERPS_INSTANCE_ENABLE_STATUS

0x8008

1

HEX

·     0—false

·     1—true

N/A

MODBUS_REG_ADDR_ERPS_PORT0_PORT_ROLE

0x8009

1

HEX

·     0—RPL.

·     1—Non-RPL.

·     2—Undefined

N/A

MODBUS_REG_ADDR_ERPS_PORT0_PORT_STATUS

0x800A

1

HEX

·     0—Block

·     1—Up

·     2—Down

·     3—Undefined

N/A

MODBUS_REG_ADDR_ERPS_PORT1

0x800B

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_ERPS_PORT1_PORT_STATUS

0x800C

1

HEX

·     0—Block

·     1—Up

·     2—Down

·     3—Undefined

N/A

 

NOTE:

·     The start ring ID is 8 and the start instance ID is 1.

·     The node data address for each ring = node start address + 0x243 * (ring ID - start ring ID).

·     The node address for an ERPS instance = node start address + (0x243 * (ring ID - start ring ID) ) + (0x9 * (instance ID - start instance ID)).

 

RRPP information (1-2) (0X9000-0x9FFF)

Node name

Start address (hex)

Data length

Unit: words

Data type

Description

Remarks

MODBUS_REG_ADDR_RRPP_PROTOCOL_STATUS

0x9000

1

HEX

·     0—disable

·     1—enable

N/A

MODBUS_REG_ADDR_RRPP_DOMAIN_ID

0x9001

1

HEX

Value range: 1 to 8

The data length for each RRPP domain is 0x582.

The start domain ID is 1.

The node data address for each domain = node start address + 0x582 * (domain ID - start domain ID).

MODBUS_REG_ADDR_RRPP_CONTROL_VLAN

0x9002

1

HEX

Value range: 2 to 4094

N/A

MODBUS_REG_ADDR_RRPP_RING_ID

0x9003

1

HEX

Value range: 1 to 128

The data length for each RRPP ring is 0xB.

The start domain ID is 1.

The start ring ID is 1.

The node data address for each RRPP ring = node start address + 0x582 * (domain ID - start domain ID) + 0xB * (ring ID - start ring ID).

MODBUS_REG_ADDR_RRPP_NODE_MODE

0x9004

1

HEX

·     0—transit

·     1—master

·     2—edge

·     3—assistant edge

N/A

MODBUS_REG_ADDR_RRPP_PRIMARY_PORT

0x9005

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_PRIMARY_PORT_STATUS

0x9006

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_SECONDARY_PORT

0x9007

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_SECONDARY_PORT_STATUS

0x9008

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_EDGE_PORT

0x9009

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_EDGE_PORT_STATUS

0x900A

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_RING_LEVEL

0x900B

1

HEX

·     0—major ring

·     1—sub ring

N/A

MODBUS_REG_ADDR_RRPP_RING_ENABLE

0x900C

1

HEX

·     0—false

·     1—true

N/A

MODBUS_REG_ADDR_RRPP_RING_STATE

0x900D

1

HEX

·     0—Completed

·     1—Failed

·     2—LinkUp

·     3—LinkDown

·     4—PreForward

·     5—LinkUpNotify

·     6—LinkDnNotify

·     7—PreForwardNotify

·     8—Unknown

N/A

 

NOTE:

·     The start domain ID and start instance ID are both 1.

·     The node data address for each domain = node start address + 0x582 * (domain ID - start domain ID).

·     The node data address for each instance = node start address +  (0x582 * (domain ID - start domain ID)) + (0xB * (ring ID - start ring ID)).

 

RRPP information (3-4) (0XA000-0xAFFF)

Node name

Start address (hex)

Data length

Unit: words

Data type

Description

Remarks

MODBUS_REG_ADDR_RRPP_DOMAIN_ID

0xA001

1

HEX

Value range: 1 to 8

The data length for each RRPP domain is 0x582.

The start domain ID is 3.

The node data address for each domain = node start address + 0x582 * (domain ID - start domain ID).

MODBUS_REG_ADDR_RRPP_CONTROL_VLAN

0xA002

1

HEX

Value range: 2 to 4094

N/A

MODBUS_REG_ADDR_RRPP_RING_ID

0xA003

1

HEX

Value range: 1 to 128

The data length for each RRPP ring is 0xB.

The start domain ID is 3.

The start ring ID is 1.

The node data address for each RRPP ring = node start address + 0x582 * (domain ID - start domain ID) + 0xB * (ring ID - start ring ID).

MODBUS_REG_ADDR_RRPP_NODE_MODE

0xA004

1

HEX

·     0—transit

·     1—master

·     2—edge

·     3—assistant edge

N/A

Master Port

MODBUS_REG_ADDR_RRPP_PRIMARY_PORT

0xA005

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_PRIMARY_PORT_STATUS

0xA006

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_SECONDARY_PORT

0xA007

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_SECONDARY_PORT_STATUS

0xA008

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_EDGE_PORT

0xA009

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_EDGE_PORT_STATUS

0xA00A

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_RING_LEVEL

0xA00B

1

HEX

·     0—major ring

·     1—sub ring

N/A

MODBUS_REG_ADDR_RRPP_RING_ENABLE

0xA00C

1

HEX

·     0—false

·     1— true

N/A

MODBUS_REG_ADDR_RRPP_RING_STATE

0xA00D

1

HEX

·     0—Completed

·     1—Failed

·     2—LinkUp

·     3—LinkDown

·     4—PreForward

·     5—LinkUpNotify

·     6—LinkDnNotify

·     7—PreForwardNotify

·     8—Unknown

N/A

 

NOTE:

·     The start domain ID is 3 and the start ring ID is 1.

·     The node data address for each domain = node start address + 0x582 * (domain ID - start domain ID).

·     The node data address for an instance = node start address + (0x582 * (domain ID - start domain ID)) + (0xB * (ring ID - start ring ID)).

 

RRPP information (5-6) (0XB000-0xBFFF)

Node name

Start address (hex)

Data length

Unit: words

Data type

Description

Remarks

MODBUS_REG_ADDR_RRPP_DOMAIN_ID

0xB001

1

HEX

Value range: 1 to 128

The data length for each RRPP domain is 0x582.

The start domain ID is 5.

The node data address for each domain = node start address + 0x582 * (domain ID - start domain ID).

MODBUS_REG_ADDR_RRPP_CONTROL_VLAN

0xB002

1

HEX

Value range: 2 to 4094

N/A

MODBUS_REG_ADDR_RRPP_RING_ID

0xB003

1

HEX

Value range: 1 to 128

The data length for each RRPP ring is 0xB.

The start domain ID is 5.

The start ring ID is 1.

The node data address for each RRPP ring = node start address + 0x582 * (domain ID - start domain ID) + 0xB * (ring ID - start ring ID).

MODBUS_REG_ADDR_RRPP_NODE_MODE

0xB004

1

HEX

·     0—transit

·     1—master

·     2—edge

·     3—assistant edge.

N/A

MODBUS_REG_ADDR_RRPP_PRIMARY_PORT

0xB005

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_PRIMARY_PORT_STATUS

0xB006

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_SECONDARY_PORT

0xB007

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_SECONDARY_PORT_STATUS

0xB008

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_EDGE_PORT

0xB009

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_EDGE_PORT_STATUS

0xB00A

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_RING_LEVEL

0xB00B

1

HEX

·     0—major ring

·     1—sub ring

N/A

MODBUS_REG_ADDR_RRPP_RING_ENABLE

0xB00C

1

HEX

·     0— false

·     1— true

N/A

MODBUS_REG_ADDR_RRPP_RING_STATE

0xB00D

1

HEX

·     0—Completed

·     1—Failed

·     2—LinkUp

·     3—LinkDown

·     4—PreForward

·     5—LinkUpNotify

·     6—LinkDnNotify

·     7—PreForwardNotify

·     8—Unknown

N/A

 

NOTE:

·     The start domain ID is 5 and the start ring ID is 1.

·     The node data address for each domain = node start address + 0x582 * (domain ID - start domain ID).

·     The node data address for an instance = node start address + (0x582 * (domain ID - start domain ID)) + (0xB * (ring ID - start ring ID)).

 

RRPP information (7-8) (0XC000-0xCFFF)

Node name

Start address (hex)

Data length

Unit: words

Data type

Description

Remarks

MODBUS_REG_ADDR_RRPP_DOMAIN_ID

0xC001

1

HEX

Value range: 1 to 128

The data length for each RRPP domain is 0x582.

The start domain ID is 7.

The node data address for each domain = node start address + 0x582 * (domain ID - start domain ID).

MODBUS_REG_ADDR_RRPP_CONTROL_VLAN

0xC002

1

HEX

Value range: 2 to 4094

N/A

MODBUS_REG_ADDR_RRPP_RING_ID

0xC003

1

HEX

Value range: 1 to 128

The data length for each RRPP ring is 0xB.

The start domain ID is 7.

The start ring ID is 1.

The node data address for each RRPP ring = node start address + 0x582 * (domain ID - start domain ID) + 0xB * (ring ID - start ring ID).

MODBUS_REG_ADDR_RRPP_NODE_MODE

0xC004

1

HEX

·     0—transit

·     1—master

·     2—edge

·     3—assistant edge

N/A

MODBUS_REG_ADDR_RRPP_PRIMARY_PORT

0xC005

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_PRIMARY_PORT_STATUS

0xC006

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_SECONDARY_PORT

0xC007

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_SECONDARY_PORT_STATUS

0xC008

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_EDGE_PORT

0xC009

1

HEX

Value range: 1 to 128

N/A

MODBUS_REG_ADDR_RRPP_EDGE_PORT_STATUS

0xC00A

1

HEX

·     0—down

·     1—up

·     2—blocked

N/A

MODBUS_REG_ADDR_RRPP_RING_LEVEL

0xC00B

1

HEX

·     0—major ring

·     1—sub ring

N/A

MODBUS_REG_ADDR_RRPP_RING_ENABLE

0xC00C

1

HEX

·     0— false

·     1— true

N/A

MODBUS_REG_ADDR_RRPP_RING_STATE

0xC00D

1

HEX

·     0—Completed

·     1—Failed

·     2—LinkUp

·     3—LinkDown

·     4—PreForward

·     5—LinkUpNotify

·     6—LinkDnNotify

·     7—PreForwardNotify

·     8—Unknown

N/A

 

NOTE:

·     The start domain ID is 7 and the start ring ID is 1.

·     The node data address for each domain = node start address + 0x582 * (domain ID - start domain ID).

·     The node data address for an instance = node start address + (0x582 * (domain ID - start domain ID)) + (0xB * (ring ID - start ring ID)).

 

 


Modbus relay

About Modbus relay

Typically, a Modbus client resides on the Ethernet network and sends Modbus-TCP messages. Modbus servers are connected via serial links and can identify only Modbus-RTU messages. As a result, the Modbus client cannot directly communicate with the Modbus servers. An H3C industrial switch acts as a relay gateway, enabling Modbus messages to be successfully exchanged between the client and servers, as shown in Figure 6.

Figure 6 Network diagram

Operating mechanism of the Modbus relay gateway

On a Modbus network, an H3C industrial switch physically connects to a Modbus client via an Ethernet interface and to Modbus servers via an RS485 serial interface. The switch must establish a TCP or UDP connection with the Modbus client so that the Ethernet TCP/IP network can carry Modbus messages. The switch also uses an RS485 serial interface to support the Modbus protocol. The RS485 serial interface enables the switch to establish a TCP or UDP connection and Ethernet communication with the Modbus client and serial communication with the Modbus servers.

An RS485 serial interface supports the following forwarding modes:

·     Transparent mode—Typically, a Modbus client sends Modbus-TCP messages. However, a high-performance Modbus client can directly generate Modbus-RTU messages when it detects that a Modbus server supports only Modbus-RTU messages. The Modbus client then sends Modbus-RTU messages to the H3C industrial switch via the TCP/IP Ethernet path, as shown in Figure 7.

In transparent mode, an RS485 serial interface on the H3C industrial switch transparently transmits Modbus-RTU messages between the Modbus client and Modbus servers.

Figure 7 Transparent mode of the relay gateway

·     Agent mode—An RS485 serial interface on the H3C industrial switch converts the Modbus-TCP messages received from a Modbus client to Modbus-RTU messages, and then forwards the converted messages to Modbus servers. The switch changes the Modbus-RTU messages received from a Modbus server to Modbus-TCP messages, and then forwards the converted messages to the Modbus client, as shown in Figure 8.

Figure 8 Agent mode of the relay gateway

The correspondence between the forwarding mode and the transport layer connection established for RS485 serial interfaces is as listed in Table 1.

Table 1 Correspondence between the forwarding mode and the transport layer connection for RS485 serial interfaces

Forwarding mode

Transport layer connection to be established

Transparent mode

As Modbus-RTU messages have no requirements for the transport layer protocol on the Ethernet network, an RS485 serial interface can establish both TCP and UDP connections with the client. In addition, the RS485 serial interface can act as either the client or server during the establishment of TCP and UDP connections.

Agent mode

The Modbus-TCP protocol supports only TCP, so an RS485 serial interface must establish a TCP connection with the client, and must act as the TCP server.

Modbus relay tasks at a glance

To configure Modbus relay, perform the following tasks:

1.     Configuring operating parameters of an RS485 serial interface

2.     Enabling Modbus and specifying the Modbus mode

3.     Configure an RS485 serial interface to establish a TCP or UDP connection with the client

¡     Configuring an RS485 serial interface to establish a TCP connection with a Modbus client

¡     Configuring an RS485 serial interface to establish a UDP connection with a Modbus client

Only one type of connection can be configured for an RS485 serial interface. You can repeat the steps on multiple RS485 serial ports to establish multiple connections.

4.     (Optional.) Optimizing Modbus performance

5.     Restoring the default settings for an RS485 serial interface

Configuring operating parameters of an RS485 serial interface

About RS485 serial interfaces

An industrial switch acts as a relay device for Modbus protocol communication between the client and servers. The switch establishes a physical connection with a Modbus server via an RS485 serial interface. To ensure connectivity of RS485 links, make sure the parameters of the RS485 serial interface matches those for the industrial switch.

Procedure

1.     Enter system view.

system-view

2.     Enter RS485 serial interface view.

interface uart interface-number

3.     Configure the description for the RS485 serial interface.

description text

By default, the description for an interface is interface name Interface (for example, UART1/0/1 Interface).

4.     Configure the flow control mode.

flow-control none

By default, no flow control mode is configured for an RS485 serial interface.

5.     Set the baud rate.

baudrate baudrate-value

By default, the baud rate is 9600 bps.

6.     Specify the number of data bits

databits 8

By default, the number of data bits is 8.

7.     Specify the number of stop bits.

stopbits { 1 | 2 }

By default, the number of stop bits for an RS485 serial interface is 1.

8.     Specify the parity.

parity none

By default, the setting is none. No parity is used.

Enabling Modbus and specifying the Modbus mode

About this task

After you specify the forwarding mode for an RS485 serial interface, Modbus on this interface is enabled.

Restrictions and guidelines

You cannot edit the forwarding mode for an RS485 serial interface by repeating the modbus mode command. To edit the forwarding mode, execute the undo modbus mode command to remove the forwarding mode configuration, and then execute the modbus mode command to reconfigure the forwarding mode.

Executing the undo modbus mode command will restore the Modbus configuration to the factory defaults, which might cause a Modbus communication interruption.

Procedure

1.     Enter system view.

system-view

2.     Enter RS485 serial interface view.

interface uart interface-number

3.     Enable Modbus and specify a forwarding mode for the RS485 serial interface and enter the corresponding Modbus mode view.

¡     Specify the agent mode for the RS485 serial interface and enter the Modbus agent mode view.

modbus mode agent

¡     Specify the transparent mode for the RS485 serial interface and enter the Modbus transparent mode view.

modbus mode raw

By default, no forwarding mode is specified for an RS485 serial interface. This indicates that the RS485 serial interface is disabled with Modbus and cannot process Modbus messages.

Configuring an RS485 serial interface to establish a TCP connection with a Modbus client

About this task

In agent mode, an H3C industrial switch acts as a Modbus server for a Modbus client and needs to receive Modbus-TCP messages from the client. Then, a TCP server connection is required. In transparent mode, an RS485 serial interface on an H3C industrial switch can act as a TCP server or TCP client to establish a TCP connection with a Modbus client for reliable transparent transmission of Modbus-RTU messages.

You can execute the modbus packet-size command to edit the minimum length of TCP packets that an RS485 serial interface sends to a Modbus client, accommodating various network environments. Increasing the minimum length enables multiple messages to be encapsulated into one TCP packet, which reduces system resource consumption caused by multiple packet encapsulations.

Restrictions and guidelines

You can configure this feature multiple times to configure an RS485 interface as a TCP client to establish TCP connections with a maximum of four Modbus clients. Do not specify TCP or UDP servers that have the same IP address for different RS485 serial interfaces on the device.

The tcp client, tcp server, udp client, and udp server commands are mutually exclusive. Do not execute two or more of these commands in the same view.

To ensure correct operation of Modbus and other services, specify an unused port number.

Configuring an RS485 serial interface as a TCP server to establish a TCP connection with a Modbus client

1.     Enter system view.

system-view

2.     Enter RS485 serial interface view.

interface uart interface-number

3.     (Optional.) Set the minimum length of TCP packets that an RS485 serial interface sends to a Modbus client.

modbus packet-size size

By default, the minimum length of TCP packets that an RS485 serial interface sends to a Modbus client is not configured. The TCP packet length varies by actual data size.

4.     Enter the Modbus transparent mode view or Modbus agent mode view.

modbus mode { agent | raw }

5.     Configure an RS485 serial interface as a TCP server to establish a TCP connection with a Modbus client (TCP client).

tcp server [ server-port server-port ] [ vpn-instance vpn-instance-name ]

By default, no role is configured for an RS485 serial interface in establishing a transport layer connection. The interface does not establish any connection with a Modbus client at the transport layer.

Configuring an RS485 serial interface as a TCP client to establish a TCP connection with a Modbus client

1.     Enter system view.

system-view

2.     Enter RS485 serial interface view.

interface uart interface-number

3.     (Optional.) Set the minimum length of TCP packets that an RS485 serial interface sends to a Modbus client.

modbus packet-size size

By default, the minimum length of TCP packets that an RS485 serial interface sends to a Modbus client is not configured. The TCP packet length varies by actual data size.

4.     Enter the Modbus transparent view.

modbus mode raw

5.     Configure an RS485 serial interface as a TCP client to establish a TCP connection with a Modbus client (TCP server).

tcp client server-ip server-ip server-port server-port [ vpn-instance vpn-instance-name ]

By default, no role is configured for an RS485 serial interface in establishing a transport layer connection. The interface does not establish any connection with a Modbus client at the transport layer.

Configuring an RS485 serial interface to establish a UDP connection with a Modbus client

About this task

The Modbus-TCP transmission mode depends on the TCP protocol. During the establishment of a UDP connection between an RS485 serial interface and a Modbus client, only transparent mode can be used to transmit Modbus-RTU messages. Establishing a UDP connection is efficient in message transmission.

Restrictions and guidelines

You can configure this feature multiple times to configure an RS485 serial interface to establish UDP connections with a maximum of four Modbus clients. Do not specify TCP or UDP servers that have the same IP addresses for different RS485 serial interfaces on the device.

The tcp client, tcp server, udp client, and udp server commands are mutually exclusive. Do not execute two or more of these commands in the same view.

To ensure correct operation of Modbus and other services, specify an unused port number.

Configuring an RS485 serial interface as a UDP server to establish a UDP connection with a Modbus client

1.     Enter system view.

system-view

2.     Enter RS485 serial interface view.

interface uart interface-number

3.     Enter the Modbus transparent view.

modbus mode raw

4.     Configure an RS485 serial interface as a UDP server to establish a UDP connection with a Modbus client (UDP client)

udp server [ server-port server-port ] [ vpn-instance vpn-instance-name ]

By default, no role is configured for an RS485 serial interface in establishing a transport layer connection. The interface does not establish any connection with a Modbus client at the transport layer.

Configuring an RS485 serial interface as a UDP client to establish a UDP connection with a Modbus client

1.     Enter system view.

system-view

2.     Enter RS485 serial interface view.

interface uart interface-number

3.     Enter the Modbus transparent view.

modbus mode raw

4.     Configure an RS485 serial interface as a UDP client to establish a UDP connection with a Modbus client (UDP server).

udp client server-ip server-ip server-port server-port [ local-port local-port ] [ vpn-instance vpn-instance-name ]

By default, no role is configured for an RS485 serial interface in establishing a transport layer connection. The interface does not establish any connection with a Modbus client at the transport layer.

Optimizing Modbus performance

Configuring minimum interval for an RS485 serial interface to send Modbus-RTU messages to a Modbus server

About this task

Modbus servers vary in type and their ability to process Modbus-RTU messages also differs. For low-performance Modbus servers, set a long Modbus-RTU message sending interval to avoid packet congestion. For high-performance Modbus servers, set a short Modbus-RTU message sending interval to accelerate the speed at which a Modbus client receives responses.

Procedure

1.     Enter system view.

system-view

2.     Enter RS485 serial interface view.

interface uart interface-number

3.     Configure the minimum interval for the RS485 serial interface to send Modbus-RTU messages to a Modbus server.

modbus packet-time interval

By default, an RS485 serial interface sends Modbus-RTU messages to a Modbus server at least every 100 milliseconds.

Restoring the default settings for an RS485 serial interface

Restrictions and guidelines

CAUTION

CAUTION:

The default command might interrupt ongoing network services. Make sure you are fully aware of the impact of this command when you use it on a live network.

This feature might fail to restore the default settings for some commands because of command dependencies or system restrictions. You can use the display this command in interface view to identify these commands, and use their undo forms or follow the Modbus command reference to restore their default settings. If your restoration attempt still fails, follow the error message instructions to solve the problem.

Procedure

1.     Enter system view.

system-view

2.     Enter RS485 serial interface view.

interface uart interface-number

3.     Restore the default settings for the RS485 serial interface.

default

Display and maintenance commands for Modbus relay

Execute display commands in any view.

Task

Command

Display information about RS485 serial interfaces.

display interface [ uart [ interface-number ] ] [ brief [ description ] ]

Display TCP sessions for an RS485 serial interface.

display modbus session [ interface interface-type interface-number ]

 

  • Cloud & AI
  • InterConnect
  • Intelligent Computing
  • Intelligent Storage
  • Security
  • SMB Products
  • Intelligent Terminal Products
  • Product Support Services
  • Technical Service Solutions
All Services
  • Resource Center
  • Policy
  • Online Help
  • Technical Blogs
All Support
  • Become A Partner
  • Partner Policy & Program
  • Global Learning
  • Partner Sales Resources
  • Partner Business Management
  • Service Business
All Partners
  • Profile
  • News & Events
  • Online Exhibition Center
  • Contact Us
All About Us
新华三官网