- 04-Layer 3—IP Services Command Reference
- 01-ARP commands
- 02-IP addressing commands
- 03-DHCP commands
- 04-DNS commands
- 05-mDNS relay commands
- 06-mDNS gateway commands
- 07-IP forwarding basics commands
- 08-Fast forwarding commands
- 09-Adjacency table commands
- 10-IRDP commands
- 11-IP performance optimization commands
- 12-UDP helper commands
- 13-IPv6 basics commands
- 14-DHCPv6 commands
- 15-IPv6 fast forwarding commands
- 16-Tunneling commands
- 17-GRE commands
- 18-HTTP redirect commands
16-Tunneling commands | 133.04 KB |
Tunneling commands
bandwidth
Use bandwidth to set the expected bandwidth for an interface.
bandwidth bandwidth-value
undo bandwidth
The expected bandwidth (in kbps) is the interface maximum rate divided by 1000.
Tunnel interface view
bandwidth-value: Specifies the expected bandwidth, in the range of 1 to 400000000 kbps.
The expected bandwidth for an interface affects the link costs in OSPF, OSPFv3, and IS-IS. For more information, see Layer 3—IP Routing Configuration Guide.
# Set the expected bandwidth for Tunnel 1 to 100 kbps.
[Sysname] interface tunnel 1
[Sysname-Tunnel1] bandwidth 100
default
Use default to restore the default settings for a tunnel interface.
default
CAUTION: The default command might interrupt ongoing network services. Make sure you are fully aware of the impact of this command when you use it on a live network. |
This command might fail to restore the default settings for some commands for reasons such as command dependencies or system restrictions. Use the display this command in interface view to identify these commands. Use their undo forms or follow the command reference to restore their default settings. If your restoration attempt still fails, follow the error message instructions to resolve the problem.
# Restore the default settings of Tunnel 1.
[Sysname-Tunnel1] default
description
The description of a tunnel interface is Tunnelnumber Interface, for example, Tunnel1 Interface.
Configure descriptions for different interfaces for identification and management purposes.
You can use the display interface command to display the configured interface description.
# Configure the description of Tunnel 1 as tunnel1.
[Sysname-Tunnel1] description tunnel1
display interface tunnel
destination
Use destination to specify the destination address for a tunnel interface.
Use undo destination to restore the default.
destination { ipv4-address | ipv6-address }
undo destination
No tunnel destination address is configured.
ipv4-address: Specifies the tunnel destination IPv4 address.
ipv6-address: Specifies the tunnel destination IPv6 address.
The tunnel destination address must be the address of the receiving interface on the tunnel peer. It is used as the destination address of tunneled packets.
The destination address of the local tunnel interface must be the source address of the peer tunnel interface. The source address of the local tunnel interface must be the destination address of the peer tunnel interface.
Do not specify the same tunnel source and destination addresses for the tunnel interfaces on the same device.
# VLAN-interface 100 on Sysname 1 uses the IP address 193.101.1.1 and VLAN-interface 100 on Sysname 2 uses the IP address 192.100.1.1. Configure the source address 193.101.1.1 and destination address 192.100.1.1 for the tunnel interface on Sysname 1.
<Sysname1> system-view
[Sysname1] interface tunnel 1 mode ipv6-ipv4
[Sysname1-Tunnel1] source 193.101.1.1
[Sysname1-Tunnel1] destination 192.100.1.1
# Configure the source address 192.100.1.1 and destination address 193.101.1.1 for the tunnel interface on Sysname 2.
<Sysname2> system-view
[Sysname2] interface tunnel 1 mode ipv6-ipv4
[Sysname2-Tunnel1] source 192.100.1.1
[Sysname2-Tunnel1] destination 193.101.1.1
interface tunnel
source
Use display interface tunnel to display tunnel interface information.
display interface [ tunnel [ number ] ] [ brief [ description | down ] ]
tunnel [ number ]: Specifies a tunnel interface. The number argument specifies the tunnel interface number. The specified tunnel interface must have been created. If you do not specify the tunnel keyword, this command displays information about all interfaces on the device. If you specify the tunnel keyword without the number argument, this command displays information about all existing tunnel interfaces.
description: Displays complete interface descriptions. If you do not specify this keyword, the command displays only the first 27 characters of interface descriptions.
down: Displays information about interfaces in the physical state of DOWN and the causes. If you do not specify this keyword, the command displays information about interfaces in all states.
# Display detailed information about Tunnel 1.
<Sysname> display interface tunnel 1
Tunnel1
Current state: UP
Line protocol state: UP
Bandwidth: 64kbps
Maximum transmission unit: 1476
Tunnel source 2002::1:1 (Vlan-interface10), destination 2001::2:1
Tunnel TOS 0xC8, Tunnel TTL 255
Tunnel protocol/transport GRE/IPv6
GRE key disabled
Checksumming of GRE packets disabled
Tunnel1 |
Information about the tunnel interface Tunnel 1. |
Current state |
Physical link state of the tunnel interface: · Administratively DOWN—The interface has been shut down by using the shutdown command. · DOWN—The interface is administratively up, but its physical state is down (possibly because no physical link exists or the link has failed). · UP—The interface is both administratively and physically up. |
Line protocol state |
Data link layer state of the interface. The state is determined through automatic parameter negotiation at the data link layer. · UP—The data link layer protocol is up. · UP (spoofing)—The data link layer protocol is up, but the link is an on-demand link or does not exist. This attribute is typical of null interfaces and loopback interfaces. · DOWN—The data link layer protocol is down. |
Description of the tunnel interface. |
Bandwidth |
Expected bandwidth of the tunnel interface. |
Maximum transmission unit |
MTU of the tunnel interface. |
Internet protocol processing: Disabled |
The tunnel interface is not assigned an IP address and cannot process IP packets. |
Internet address: ip-address/mask-length (Type) |
IP address of the interface and type of the address in parentheses. Possible IP address types include: · Primary—Manually configured primary IP address. · Sub—Manually configured secondary IP address. If the interface has both primary and secondary IP addresses, the primary IP address is displayed. If the interface has only secondary IP addresses, the lowest secondary IP address is displayed. · Unnumbered—IP address borrowed from another interface. |
Tunnel source |
Source address of the tunnel. If a source interface is specified for the tunnel interface, this field also displays the source interface in parentheses. |
destination |
Destination address of the tunnel. |
Tunnel TOS |
ToS of tunneled packets. |
Tunnel TTL |
TTL of tunneled packets. |
Tunnel protocol/transport |
Tunnel mode and transport protocol: · GRE/IP—GRE/IPv4 tunnel mode. · GRE/IPv6—GRE/IPv6 tunnel mode. · IP/IP—IPv4 over IPv4 tunnel mode. · IP/IPv6—IPv4 over IPv6 tunnel mode. · IPv6/IP—IPv6 over IPv4 manual tunnel mode. · IPv6/IP 6to4—IPv6 over IPv4 6to4 tunnel mode. · IPv6/IP ISATAP—IPv6 over IPv4 ISATAP tunnel mode. · IPv6/IPv6—IPv6 over IPv6 tunnel mode. · UDP_VXLAN/IP—UDP-encapsulated IPv4 VXLAN tunnel mode. · UDP_VXLAN/IPv6—UDP-encapsulated IPv6 VXLAN tunnel mode. |
GRE key disabled |
No GRE tunnel interface key is configured. |
Checksumming of GRE packets disabled |
The GRE packet checksum feature is disabled. |
Last clearing of counters |
Last time when counters were cleared. |
Last 300 seconds input rate: 0 bytes/sec, 0 bits/sec, 0 packets/sec |
Average input rate in the last 300 seconds. |
Last 300 seconds output rate: 0 bytes/sec, 0 bits/sec, 0 packets/sec |
Average output rate in the last 300 seconds. |
Input: 0 packets, 0 bytes, 0 drops |
Total input packets, total input bytes, and total input packets dropped. Input packets are counted after they are de-encapsulated by software. |
Output: 0 packets, 0 bytes, 0 drops |
Total output packets, total output bytes, and total output packets dropped. Output packets are counted before they are encapsulated by software. |
# Display brief information about Tunnel 1.
<Sysname> display interface tunnel 1 brief
Protocol: (s) - spoofing
Tun1 UP UP 1.1.1.1 aaaaaaaaaaaaaaaaaaaaaaaaaaa
# Display brief information about Tunnel 1, including the complete interface description.
<Sysname> display interface tunnel 1 brief description
Tun1 UP UP 1.1.1.1 aaaaaaaaaaaaaaaaaaaaaaaaaaaaa
Aaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaaa
# Display information about interfaces in DOWN state and the causes.
<Sysname> display interface tunnel brief down
Interface Link Cause
Tun0 DOWN Not connected
Tun1 DOWN Not connected
Abbreviated interface name. |
Link |
Physical link state of the interface: · UP—The interface is physically up. · DOWN—The interface is physically down. · ADM—The interface has been shut down by using the shutdown command. To restore the physical state of the interface, use the undo shutdown command. · Stby—The interface is a backup interface in standby state. |
Protocol |
Data link layer protocol state of the interface: · UP—The data link layer protocol of the interface is up. · DOWN—The data link layer protocol of the interface is down. · UP(s)—The data link layer protocol of the interface is up, but the link is an on-demand link or does not exist. The (s) attribute represents the spoofing flag. This value is typical of null interfaces and loopback interfaces. |
Primary IP |
Primary IP address of the interface. This field displays two hyphens (--) if the interface does not have an IP address. |
Description of the interface. |
Cause |
Cause for the physical link state of an interface to be DOWN: · Administratively—The interface has been manually shut down by using the shutdown command. To restore the physical state of the interface, use the undo shutdown command. · Not connected—The tunnel is not established. |
destination
interface tunnel
source
interface tunnel
Use interface tunnel to create a tunnel interface, specify the tunnel mode, and enter tunnel interface view, or enter the view of an existing tunnel interface.
Use undo interface tunnel to delete a tunnel interface.
interface tunnel number [ mode { gre [ ipv6 ] | ipv4-ipv4 | ipv4-ipv6 | ipv6-ipv4 [ 6to4 | isatap ]| ipv6-ipv6 |vxlan [ ipv6 ] } ]
undo interface tunnel number
No tunnel interfaces exist.
number: Specifies the number of the tunnel interface. The value range for tunnel interface numbers is 0 to 2047 for the S6812 switch series and 0 to 4095 for the S6813 switch series. The number of tunnel interfaces that can be created is restricted by the total number of interfaces and the memory.
mode gre: Specifies the GRE/IPv4 tunnel mode.
mode gre ipv6: Specifies the GRE/IPv6 tunnel mode.
mode ipv4-ipv4: Specifies the IPv4 over IPv4 tunnel mode.
mode ipv4-ipv6: Specifies the IPv4 over IPv6 tunnel mode.
mode ipv6-ipv4: Specifies the IPv6 over IPv4 manual tunnel mode.
mode ipv6-ipv4 6to4: Specifies the 6to4 tunnel mode.
mode ipv6-ipv4 isatap: Specifies the ISATAP tunnel mode.
mode ipv6-ipv6: Specifies the IPv6 over IPv6 tunnel mode.
mode vxlan: Specifies the IPv4 VXLAN tunnel mode.
mode vxlan ipv6: Specifies the IPv6 VXLAN tunnel mode.
To create a new tunnel interface, you must specify the tunnel mode in this command. To enter the view of an existing tunnel interface, you do not need to specify the tunnel mode.
A tunnel interface number is locally significant. The tunnel interfaces on the two ends of a tunnel can use the same or different interface numbers.
On IPv4 and IPv6 VXLAN tunnel interfaces, IP addresses (assigned by ip address and ipv6 address commands) are meaningless. As a best practice, do not assign IP addresses to those types of tunnel interfaces.
# Create GRE/IPv4 tunnel interface Tunnel 1 and enter tunnel interface view.
[Sysname] interface tunnel 1 mode gre
[Sysname-Tunnel1]
destination
source
mtu
Use mtu to set the MTU on a tunnel interface.
mtu size
undo mtu
If the tunnel interface has never been up, the MTU is 64000 bytes.
If the tunnel interface is up, its MTU is identical to the outgoing interface's MTU minus the length of the tunnel headers. The outgoing interface is automatically obtained through routing table lookup based on the tunnel destination address.
size: Specifies the MTU, in the range of 100 to 64000 bytes.
If you do not configure an MTU for a tunnel interface or the configured MTU is 64000 bytes, the effective MTU depends on the tunnel interface status.
· If the tunnel interface is up, its MTU is identical to the outgoing interface's MTU minus the length of the tunnel headers.
· If the tunnel interface is down, the device does not calculate or update the MTU of the tunnel interface.
If you configure an MTU for a tunnel interface and the MTU is not 64000 bytes, the configured MTU applies regardless of the tunnel interface status (up/down) and the outgoing interface MTU.
To avoid fragmentation after tunnel encapsulation, set the tunnel interface MTU no greater than the value of the outgoing interface MTU minus the length of the tunnel headers.
You can use the ip mtu, ipv6 mtu, or mtu command to set the MTU of a tunnel interface.
· The mtu command applies to both IPv4 and IPv6 tunnel interfaces.
· The ip mtu and ipv6 mtu commands have higher priority than the mtu command on a tunnel interface.
· If all of the commands are used on a tunnel interface, the ip mtu and ipv6 mtu commands take effect. After you restore the default settings for the ip mtu and ipv6 mtu commands, the mtu command takes effect.
· If none of the commands is used on a tunnel interface, the MTU of the tunnel interface is identical to the outgoing interface's MTU minus the length of the tunnel headers. The outgoing interface is automatically obtained through routing table lookup based on the tunnel destination address.
# Set the MTU on Tunnel 1 to 10000 bytes.
[Sysname-Tunnel1] mtu 10000
ip mtu
ipv6 mtu
reset counters interface tunnel
Use reset counters interface tunnel to clear tunnel interface statistics.
reset counters interface [ tunnel [ number ] ]
tunnel [ number ]: Specifies a tunnel interface. The number argument specifies the tunnel interface number. If you do not specify the tunnel keyword, this command clears statistics for all interfaces. If you specify the tunnel keyword without the number argument, this command clears statistics for all tunnel interfaces.
Use this command to clear old statistics so you can observe new traffic statistics on a tunnel interface.
# Clear statistics for Tunnel 1.
<Sysname> reset counters interface tunnel 1
service
Use service to specify a traffic processing slot for a tunnel interface.
Use undo service to restore the default.
service slot slot-number
undo service slot
No traffic processing slot is specified for a tunnel interface.
slot slot-number: Specifies an IRF member device by its member ID.
Specify a traffic processing slot if a feature (for example, IPsec antireplay) requires that all traffic on a tunnel interface be processed on the same slot.
Make sure the specified traffic processing slot is available. If the specified traffic processing slot is unavailable, traffic on the tunnel interface cannot be forwarded, whether or not the tunnel interface is up. Traffic on the tunnel interface will not be forwarded until the traffic processing slot becomes available or until you respecify an available traffic processing slot.
# Specify a traffic processing slot for Tunnel 200.
[Sysname] interface tunnel 200
[Sysname-Tunnel200] service slot 1
shutdown
Use shutdown to shut down a tunnel interface.
Use undo shutdown to bring up a tunnel interface.
shutdown
A tunnel interface is not administratively down.
This command disconnects all links set up on the interface. Make sure you fully understand the impact of the command on your network.
# Shut down Tunnel 1.
[Sysname-Tunnel1] shutdown
source
Use source to specify the source address or source interface for a tunnel interface.
Use undo source to restore the default.
source { ipv4-address | ipv6-address | interface-type interface-number }
undo source
No source address or source interface is specified for a tunnel interface.
ipv4-address: Specifies the tunnel source IPv4 address.
ipv6-address: Specifies the tunnel source IPv6 address.
The specified source address or the address of the specified source interface is used as the source address of tunneled packets. To display the configured tunnel source address, use the display interface tunnel command.
# Specify VLAN-interface 10 as the source interface of Tunnel 1.
[Sysname-Tunnel1] source vlan-interface 10
# Specify 192.100.1.1 as the source address of Tunnel 1.
[Sysname-Tunnel1] source 192.100.1.1
destination
interface tunnel
tunnel dfbit enable
Use tunnel dfbit enable to set the Don't Fragment (DF) bit for tunneled packets.
Use undo tunnel dfbit enable to restore the default.
tunnel dfbit enable
The DF bit is not set for tunneled packets.
To avoid fragmentation and delay, set the DF bit for tunneled packets. Make sure the path MTU is larger than the tunneled packet length. To avoid discarding tunneled packets whose length is larger than the path MTU, do not set the DF bit.
This command is not supported on GRE/IPv6 tunnel interfaces, IPv4 over IPv6 tunnel interfaces, or IPv6 over IPv6 tunnel interfaces.
# Set the DF bit for tunneled packets on Tunnel 1.
[Sysname-Tunnel1] tunnel dfbit enable
tunnel tos
Use tunnel tos to set the ToS of tunneled packets.
Use undo tunnel tos to restore the default.
tunnel tos tos-value
undo tunnel tos
The ToS of tunneled packets is the same as the ToS of the original packets.
tos-value: Specifies the ToS of tunneled packets, in the range of 0 to 255.
After you configure this command, all the tunneled packets of different services sent on the tunnel interface will use the same configured ToS. For more information about ToS, see ACL and QoS Configuration Guide.
# Set the ToS of tunneled packets to 20 on Tunnel 1.
[Sysname-Tunnel1] tunnel tos 20
tunnel ttl
Use tunnel ttl to set the Time to Live (TTL) of tunneled packets.
Use undo tunnel ttl to restore the default.
tunnel ttl ttl-value
undo tunnel ttl
The TTL of tunneled packets is 255.
ttl-value: Specifies the TTL of tunneled packets, in the range of 1 to 255.
The TTL determines the maximum number of hops that the tunneled packets can pass. When the TTL expires, the tunneled packets are discarded to avoid loops.
# Set the TTL of tunneled packets to 100 on Tunnel 1.
[Sysname-Tunnel1] tunnel ttl 100
tunnel vpn-instance
Use tunnel vpn-instance to specify a VPN instance for the destination address of a tunnel interface.
Use undo tunnel vpn-instance to restore the default.
tunnel vpn-instance vpn-instance-name
The destination address of a tunnel interface belongs to the public network.
vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters.
After this command is executed, the device looks up the routing table of the specified VPN instance to forward tunneled packets on the tunnel interface.
For a tunnel interface to come up, the tunnel source and destination must belong to the same VPN instance. To specify a VPN instance for the tunnel source, use the ip binding vpn-instance command on the tunnel source interface.
The tunnel vpn-instance command is not supported on VXLAN tunnel interfaces.
# Specify VPN instance vpn10 for the tunnel destination on Tunnel 1.
[Sysname] ip vpn-instance vpn10
[Sysname-vpn-instance-vpn10] route-distinguisher 1:1
[Sysname-vpn-instance-vpn10] vpn-target 1:1
[Sysname-vpn-instance-vpn10] quit
[Sysname-Vlan-interface10] ip binding vpn-instance vpn10
[Sysname-Vlan-interface10] ip address 1.1.1.1 24
[Sysname-Vlan-interface10] quit
[Sysname-Tunnel1] destination 1.1.1.2
[Sysname-Tunnel1] tunnel vpn-instance vpn10
ip binding vpn-instance (MPLS Command Reference)